Discuss diversity on lighting circuit? in the UK Electrical Forum area at ElectriciansForums.net

S

sima24

Hi guys, was wondering if its acceptable to allow diversity to a lighting circuit. Customer has about 8 lights on the downstairs lighting circuit, but wants 12 spots putting into the kitchen. Now using the 100w per lighting point takes total current to 8.5A with all lights on at 100w. Now all the lamps are not 100w, but would i still have to split it into 2 6a circuits or can i apply diversity? Thanks
 
No diversity, but you can simply ensure that the proposed load can be carried by the circuit (cable and ocpd). You will also have to consider the need for rcd protection for the circuit, if it is not already in place.
Regards.
 
As Will says, apply a bit of common sense.
 
No diversity, but you can simply ensure that the proposed load can be carried by the circuit (cable and ocpd). You will also have to consider the need for rcd protection for the circuit, if it is not already in place.
Regards.

Why a need for a RCD? If he uses the existing switch drops and simply makes changes above the ceiling I'd suggest they aren't required.
 
Also if when you consider load on a lighting circuit can you actually buy/fit 100w bulbs any more. As others have said a dose of common sense is required.

The same can also be said about calculating maximum load when housed now often have a 10 way board rather than a 6 way board.
 
Thanks, i understand everyone would use common sense, but i changed the board in safe property a while ago and going to use for my elecsa inspection, not sure if they would use common sense or still thoroughly to the regs
 
You can apply common sense and diversity to lighting circuits-

12 x 100W = 5.2A
12 x 50W = 2.6A

So based on your information and assuming you will install 12 x 50W GU10's and that all the other points in the house are 100W or less, I would reduce your total load by 2.6A to 5.9A and then apply diversity of 66% to the 5.9A = 3.9A

Obviously all subject to satisfactory test results to existing circuit.
 
Last edited:
Guys, I might be getting this all wrong, but this talk of "diversity" is, I think, misplaced.

Diversity is used/applied when calculating the maximum demand for an installation, and is applied to the total current deman of individual circuits (e.g 66% of total current demand for lighting).

The OP has essentially asked if by increasing the number of lights/downlighters, he is going to have a problem with the load on the circuit. As others have pointed out, the circuit will have been designed at 100W per light (single pendant/room) and of course, typically modern lights have lower wattage and may even be led. So it's simply about checking the new total load against the ccc of the cable and the ocpd.

Not looking to start an argument - just want to ensure I've not been misunderstanding diversity all these years!!!!:bigcry:
 
To apply diversity to a lighting circuit is to assess the likelyhood of all the lights being on at the same time for long periods , if this is unlikely then you can apply the 66% of full load figure that the OSG suggests for domestic installations.
Commercial installations , such as offices , often have whole areas of the building lit up for long periods thus only a small diversity adjustment can be made eg 90% of full load.
The actual wattage of the lights is what you use to calculate the circuit design current , then you apply diversity after reaching this figure.
 

Reply to diversity on lighting circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
5
Views
330
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
964
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
373
Hi The ground floor of my house has two lighting circuits which are each protected by an MCB. One of those circuits is just indoor lights. The...
Replies
15
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock