Thumbing through the OSG guide today and I have a couple of questions regarding the above table.

Firstly, just a idiot check but electric showers would fall into no.5 water heaters of the instantaneous type. I know this but so often doubt myself.

Secondly, No. 9. Am I right that this would be applied across all circuits to see if the main switch and supply are big enough. Its thrown me because if that's correct I would expect it to be last in the table.

Thirdly, No 10. Good old socket outlets. When would this apply if we typically using the standard 'socket outlet' circuits. Could I apply this in a workshop where I have a welder that takes a 16A C-Form connection on a radial with other outlets e.g to a fan? If someone could provide an example that would be great.

Thanks

Chris
 
Morning all,

Thumbing through the OSG guide today and I have a couple of questions regarding the above table.

Firstly, just a idiot check but electric showers would fall into no.5 water heaters of the instantaneous type. I know this but so often doubt myself.

Secondly, No. 9. Am I right that this would be applied across all circuits to see if the main switch and supply are big enough. Its thrown me because if that's correct I would expect it to be last in the table.

Thirdly, No 10. Good old socket outlets. When would this apply if we typically using the standard 'socket outlet' circuits. Could I apply this in a workshop where I have a welder that takes a 16A C-Form connection on a radial with other outlets e.g to a fan? If someone could provide an example that would be great.

Thanks

Chris
16Amp socket on it's own circuit imo, if it takes 16Amps no diversity, a fan on the same circuit not good practice imo
 
Why?

The welder will run off a 13A plug top but prefers 16A connection for full power work at which point it has a 40% work cycle.

And in which case then - when would 10 apply?

Sorry if I'm being stuuupid.
 
Why?

The welder will run off a 13A plug top but prefers 16A connection for full power work at which point it has a 40% work cycle.

And in which case then - when would 10 apply?

Sorry if I'm being stuuupid.
If you try and run a welder rated at 16Amps from a 13 Amp socket you are asking for trouble, sorry to be so blunt.
 
I agree with Pete - a 16A socket, a 16A welder and a 16A MCB that's your lot. If the radial is 2.5 clipped direct why not increase to 20A MCB perhaps? For my humble workshop I added a length of 2.5 to make a 32A RFC and no more worries :)
 
Treat the 16A socket as such and ignore the welder you cannot use that in diversity calculations.
I know it is acceptable to connect 16A EN60309 sockets through 20A devices but I would only apply this to multiple outlets and not a single socket.
 
Thanks guys.

Lots of interesting takes on the welder problem. SteveTheSpark is right and when I bought the welder he offered to change the 16A connection to a 13A plug but I said it was OK and that I knew a tame electrician who could install a 16A for me.

If we put the welder problem aside. When would you be looking at No 10 to calculate diversity. To save you looking it up it says Socket Outlets - 100% of current demand of largest point of utilisation + 40% of current demand of every other point of utilisation.

Thanks again. As a self employed new spark its good to chew the ears off more seasoned experts and get different takes on a regulation etc.
 
Most small welders are supplied with 13 amp plug. ..... calculated that full load is for a minimal time .........

Look about at the contents of a few welder 13A plug fuse holders .
( You may be enlightened ... or the trail of discarded blown 13A fuses ) They take 26A to blow softly , just under to last a DAY/Week !
 
That doesn't surprise me at all. When I was reading about which welder to get they talked about replacing the plug regularly because it was designed to operate at the load demanded by the welder and they degrade!

Would it be right to say the manufacturers are knowingly abusing 13A plug tops in order to sell hobby welders?
 

Reply to Diversity Table A2 OSG P118 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Replies
3
Views
1K
Hey guys I really need urgent help understanding this Basically I'm trying to calculate what the diversity factor/percentages would be for the...
Replies
2
Views
5K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock