Dear All,

I am trying to calculate diversity for an installation. The DB has a 60A main fuse. TT system. Small 2 bedroom cottage. Unable to get converted to TNS

At the present time I have the following circuits
Up ring 32A MCB (2 Bedrooms)
Down ring 32A MCB (Small lounge & dining room)
Up lights 6A MCB (4 x 60W bulbs)
Down lights 6A MCB (4 x 60W Bulbs)
Immersion 16A dedicated circuit (13A fused spur/switch) 2.4kW
Air source pump 40A (nominal 15A but has potential of high start current if temp below 0 deg C)
Airsource control 6A dedicated circuit

Adding all this up, even with diversity, is well in excess of the 60A main fuse. Is there anything I can do to reduce the diversity of this installation?

It may be worth noting the following:
1. That the immersion is a back up if the air source heater fails
2. Both ring circuits will be subject to very light loads

Cheers Dave
 
Dear All,

I am trying to calculate diversity for an installation. The DB has a 60A main fuse. TT system. Small 2 bedroom cottage. Unable to get converted to TNS

At the present time I have the following circuits
Up ring 32A MCB (2 Bedrooms)
Down ring 32A MCB (Small lounge & dining room)
Up lights 6A MCB (4 x 60W bulbs)
Down lights 6A MCB (4 x 60W Bulbs)
Immersion 16A dedicated circuit (13A fused spur/switch) 2.4kW
Air source pump 40A (nominal 15A but has potential of high start current if temp below 0 deg C)
Airsource control 6A dedicated circuit

Adding all this up, even with diversity, is well in excess of the 60A main fuse. Is there anything I can do to reduce the diversity of this installation?

It may be worth noting the following:
1. That the immersion is a back up if the air source heater fails
2. Both ring circuits will be subject to very light loads

Cheers Dave


I've not done any number crunching, but if the immersion is only able to be energised when the air source pump fails, and if the air source pump truly is 15A nominal, I get around 54A.
 

Reply to Diversity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
556
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
687
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock