  1. BruceB
    Offline

    BruceB Electrician's Arms

    Location:
    Bath/Bristol
    You are probably aware of these Forms A, B and C on the MCS site:
    Microgeneration Certification Scheme - Heat Pumps
    which we have to complete prior to connecting a heat pump.

    I want to put the application in early on one of my jobs because it is a largish heat pump and in a village and I want to know early if network reinforcement is required.

    A stuff of a lot of detail on power quality harmonics, voltage fluctuation and flicker is required. I got straight through to someone sensible at Kensa who is filling it in and sending it back. Nibe just puts me on hold with muzak so have sent a request to an anonymous '[email protected]' email address.

    Where is everyone getting this info. I cannot believe all these forms are being done individually by the manufacturers. Have any of the other masnufacturers already published the data?
     
  2. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    If the heat pump is compliant to EN 6100-3-2 ns 6100-3-3 and less than 75amp it will be ok jus put down the KW rating
     
  3. BruceB
    Offline

    BruceB Electrician's Arms

    Location:
    Bath/Bristol
    EN 61000-3-2 and EN 61000-3-3 can only apply to equipment below 16A per phase. So for instance a Kensa single phase 16 kW twin compressor heat pump operates with a running current well above 16 A. Therefore EN 61000-3-11 and EN 61000-3-12 apply to it and all the detail is required.

    That's how I read it anyway.
     
  4. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    From Form A
    Use this form to apply to connect new or additional heat pump equipment rated up to 75A per phase that complies with two specific standards that cover power quality – EN 61000-3-2 and EN 61000-3-3
     
Loading...
Similar Threads - application connect heat Forum Date
Application Apply to Gain Access to Trainee-Only Forum Feb 8, 2019
Application to trainee-only forum Apply to Gain Access to Trainee-Only Forum Feb 5, 2019
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. dno application for an air source heat pump

    ,
  2. heat pumps dno

    ,
  3. Heat pump notification

Electricians Directory Post a Domestic Job Post a Commercial Job