Discuss DNO fuse 80amp, board dp 100amp in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
168
Hi hope someone can help. If a small house's DNO's fuse is rated at 80amps, is it considered bad practice to fit a db with a 100amp dp switch ? As most db's have a 100amp switch I assume this is common practice, also I expect an 80 amp DNO fuse can handle alot more before it blows.
 
772b2ad6b9d918e0ff34a302c7bed30f.png
 
make allowances for the op. he's from london. up north for thinking, down south for dancing. :eek:sama:
 
Its about time they stopped putting current rating on a switch as its way too much detail for todays electrician. What with 63A rated RCDs it can only end in disaster.

The manufacturers should hide it in the small print with a warning " Dear electrician, FFS - this is not an OPD"
 
Hi haptism, either your terminology is incorrect or your understanding of how a DP main switch operates is, if its the latter and like suggested in post 5 - you really need to research the differences between

Main DP switches
Fused switches
Switch fuses
MCCB's (with respect to front end protection)

I recommend you have a think about it before your next post..Ill have to be blunt here in saying if you don't understand the basics of operation of a DP main switch then you really shouldn't be a practising Electrician.

EDIT-
PS - Just to offer an olive branch here and some advice regarding why members have responded as such, your standard DP switch often found on your domestic CU is just that 'a switch' - it is solely for means of isolation and provides no overload or short circuit protection, it will not trip under O/L or S/C conditions.

The rating on the front is solely to indicate the max current it can handle so if the DNO fusing is 80amps then the rating of the DP switch is ample at 100amp.
 
Last edited:
Hi haptism, either your terminology is incorrect or your understanding of how a DP main switch operates is, if its the latter and like suggested in post 5 - you really need to research the differences between

Main DP switches
Fused switches
Switch fuses
MCCB's (with respect to front end protection)

I recommend you have a think about it before your next post..Ill have to be blunt here in saying if you don't understand the basics of operation of a DP main switch then you really shouldn't be a practising Electrician.

EDIT-
PS - Just to offer an olive branch here and some advice regarding why members have responded as such, your standard DP switch often found on your domestic CU is just that 'a switch' - it is solely for means of isolation and provides no overload or short circuit protection, it will not trip under O/L or S/C conditions.

The rating on the front is solely to indicate the max current it can handle so if the DNO fusing is 80amps then the rating of the DP switch is ample at 100amp.
you're getting mellow in your old age. dementia is next. :bigear:
 
Hi all, thanks for the responses, Ive been to Church just now so a bit of delay. I should mention that im no longer a working electrician (I used to be), I now work for Thames Water dealing with water. I thought I would post up this query as on a couple of occasions ive been into properties and noticed the DNO fuse has a lower rating than the db's mainswitch (100a). I was unaware :sweatdrop: that a db's dp main switch would not "trip" under O/L or S/C conditions so you have sorted that for me ! Give yourselves a pat on the back and much thanks for your info.

No dancing at church tonight but there was a good sermon about "salt of the earth"
 
Hi all, thanks for the responses, Ive been to Church just now so a bit of delay. I should mention that im no longer a working electrician (I used to be), I now work for Thames Water dealing with water. I thought I would post up this query as on a couple of occasions ive been into properties and noticed the DNO fuse has a lower rating than the db's mainswitch (100a). I was unaware :sweatdrop: that a db's dp main switch would not "trip" under O/L or S/C conditions so you have sorted that for me ! Give yourselves a pat on the back and much thanks for your info.

No dancing at church tonight but there was a good sermon about "salt of the earth"

Fair play for being honest.

I will be honest as well,and say i am still shocked. ;)
 
On that note, I think the thread be best closed as the OP has explained his position and tbh I don't see the thread can move any further forward in a constructive manner.
 

Reply to DNO fuse 80amp, board dp 100amp in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
428
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
682

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock