    Just started doing my first block of flats as a Qualified supervisor.

    I have 5 flats and a landlords supply to wire up.

    Done my calculations a while back and told the DNO I would need require ADMD of 12.5 kva for each flat which I thought was reasonable, Considering I have 3 rings, 2 lighting , 1 UFH supply and a small oven circuit.

    Just to check I phoned the NICEIC technical to reassure I done the right calcs in the Onsite guide table etc. They basically said you can make it up it's more or less common sense to the load you would achieve??

    But my dilemma is the DNO wrote this back to me but I would have thought this was a rather small supply?


    UK Power Networks would in general expect the (ADMD - after diversity
    maximum demand) for a gas heated flat/house to be between 1.5kVA and
    3.0kVA and an electric heated flat/house to be between 5kVA & 10kVA
    unless abnormal high usage appliances are being installed.
     
  2. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Yes that's in line with their network design guide,

    What's your question??
     
  3. Cadgey123
    Offline

    Cadgey123 Electrician's Arms

    Location:
    London
    Well suppose it may be why is there such a high diversity on their side of things for a supply to each flat?
     
  4. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    It's not all that high a diversity factor.

    Personally I've never measured an average demand above 20A for a domestic installation.
     
  5. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    Generally the DNO will want to supply as little as possible and for multiple properties (streets) they can apply massive diversity as people use things at different times and so it all evens out.
    For your situation you have less flexibility but even so you can expect much lower than the design current. For your list you could assess the sockets as taking no more than 10A in general (assuming they are not running electric heaters) even though there are three rings (good division of circuits) and I do not know the size of the flats mostly there will only be kettles taking significant power and then only for a very short time.
    lighting will take minimal current, especially as it should be energy efficient.
    UFH unless huge will take maybe a couple of amps.
    Oven (perhaps cooker?) circuit taking 15A for short periods.
    So maybe a total of 30A (7kVA) at maximum use and this would be for short periods so say halving this to balance across for five flats over time in general on average is close to their 3kVA.

    This is just an off the cuff example of how you might want to assess actual loading, obviously you know a lot more about the flats size and expected use which may make significant changes to the demand.
     
    • Like Like x 1
  6. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Can I ask please - what fuse size is planned for each installation?
     
  7. Cadgey123
    Offline

    Cadgey123 Electrician's Arms

    Location:
    London

    I have ran 25mm2 cables to each flat and the are relatively short runs so probably a 80amp switched fuse will fit the bill.
     
  8. Cadgey123
    Offline

    Cadgey123 Electrician's Arms

    Location:
    London

    Cheers Richard, that makes a lot of sense.
    Thanks for taking the time to explain it for another angle.
     
Loading...
Similar Threads - maximum demand message Forum Date
DCP 161 implementation April 1st and calculating KVA, maximum demand Electrical Forum Mar 20, 2018
Ze at its Maximum Measurement Electrical Wiring, Theories and Regulations Tuesday at 3:16 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job