Discuss Do I need an Electrician to replace a 30A Hob? in the Electrical Appliances Forum area at ElectriciansForums.net

Ocan

-
Reaction score
14
Hi, so 4am this morning our bedroom fan went off which woke me up - whole upstairs socket ring was out - I went downstairs and the lights ring was out. Checked the C.U and one of those double switches was in the off position - tried to reset but couldn't, decided to go back to bed!

So this morning we've checked the whole house and the hob was off - must be on the same RCD, so I put the hob isolator in the off position and presto the electrics sprung back into life! The hob is over 10 years old so we've decided to replace it - sorry for all the waffle but I figured it best to give a brief history before asking... Do I need an Electrician to fit a new hob? When we got this one fitted when we moved in we had to get an Electrician to fit it - is it the same procedure?
We're in Southport, Merseyside btw if anyone fancies a small job?
Thanks, Alan
 
Hi, so 4am this morning our bedroom fan went off which woke me up - whole upstairs socket ring was out - I went downstairs and the lights ring was out. Checked the C.U and one of those double switches was in the off position - tried to reset but couldn't, decided to go back to bed!

So this morning we've checked the whole house and the hob was off - must be on the same RCD, so I put the hob isolator in the off position and presto the electrics sprung back into life! The hob is over 10 years old so we've decided to replace it - sorry for all the waffle but I figured it best to give a brief history before asking... Do I need an Electrician to fit a new hob? When we got this one fitted when we moved in we had to get an Electrician to fit it - is it the same procedure?
We're in Southport, Merseyside btw if anyone fancies a small job?
Thanks, Alan
Tel's offer well worth taking up, if you do opt for Tel's offer, hide any thing that looks remotely like a bottle or can of Ale.:);):p:eek::rolleyes:o_O:) A joke of course.
 
Yes perhaps it is wisest to get in an electrician. If the hob is causing the RCD to trip it could possibly be the circuit it is on, not the hob necessarily. An electrician can make sure of that for you so that you know it is the hob not the circuit.
 
Nice one,Tel...but don't be disappointed when you get there,and find out it is nowhere near the Mersey :)
 
Tels a good guy, I am glad it went well, ps if your hub caps are gone you will know why lol
 
I'm guessing it wasn't straightforward ...
the hole in the worktop was shy by 10mm each way. took a lot of wood butchery to enlarge it to fit. just my luck not to have taken a jigsaw.
 
hand saw and a multitool. took over an hour to cut it out.:eek:
 
@telectrix’s working patch seems to be 150 mile radius of his pint glass - I’m sure he’s keeping this country afloat (that’s not a comment on his drinking)
It’s nice to see professionalism - from your armchair!
 

Reply to Do I need an Electrician to replace a 30A Hob? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Had a new unvented Boiler fitted as the old one had reached the end of it's life. Electrician mentioned that it might be worth replacing my fuse...
Replies
11
Views
1K
Hello, we have just had a replacement hob through warranty, the electrician who came to fit it said it needs ho5rrf cable when we have 6mm. He...
Replies
3
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Replies
2
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock