    Do you have to run separate earth with SWA which is supplying a D/B.

    Ive done the tests and the steel wire is good enough for earth.

    This job was done last year.

    Its for an industrial EICR
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    if the armour is adequate as regards csa and satisfies adiabatic. perfectly OK.

    trhere's a stcky... can i use the armour... good read.
     
  3. electricshock
    Offline

    electricshock Regular EF Member

    thanks il read the sticky
     