Does anyone know if cold weather can affect RCD's, I have just been testing the 63A 30mA RCD in the garage, this previously tested absolutely fine when doing the test at 30mA, but now it fails to trip in under 400ms, however when doing the 5x test it is fine :confused:, the test button works fine when pressed. The temperature is very low out there at the moment and I wondered if this could have an effect.

Thanks

Down2Earth
 
Im not sure, will be interested to find out. I do beleive most things are tested to work between certain temperature extremes and I dont see why an RCD would be any different, though I am thinking it would have to be very low indeed to affect opperation. Lets see what the pros have to say.
 
Rcd's can be affected by temperature and humitidy.

When PIR testing a caravan park in winter with the DB's enclosed in outdoor brick enclosures less than 5% worked properly.

Solution to this was to install a 60W tubular heater in each enclosure. Retested after heaters where installed for 2 weeks and 95% worked properly.
 

Reply to Does cold weather affect RCD's? in the Australia area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and...
Replies
24
Views
6K
Doing standard tests prior to some minor works on a socket circuit (Zs, IR etc), pressed the test button on the RCD, tripped fine, got ready to...
Replies
3
Views
5K
  • Locked
united kingdom...yorkshire I rent a semi detached house out which was built 1970's With the tenancy just changed i thought i would change the...
Replies
44
Views
4K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
12K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock