Discuss Does DNO have to maintain/provide earth? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

The Ghost

Now in TT cases obviously not. Example, attended 50's type house. TNS looped through to next door. Nothing unusual there. Next doors earth is on this house's MET in 4 mm² and not the sheath of the incoming cable. Told DNO they said "We have no responsibility to supply an earth" In any event this strikes me as wrong. As far as I understand ESQCR require the DNO to maintain the earth supply in good condition.
If a fault on earth from next door goes onto this house's earth..... As this is older type wiring and various add ons over the years, there is cross bonding on water pipes etc. and supplementary bonding etc. So this house could become live on the metal work from next door earth fault. What would you say to DNO? or customer.
 
Hi V, I understand it the same as you - the DNO is required to maintain an earth if one is provided. It is not ok to provide a substandard earthing arrangement. It can't be right to have the 2nd house on the 1st house met and the 2nd house should request their own earth from DNO or if DNO decide they won't provide one then convert to TT.
 
Now in TT cases obviously not. Example, attended 50's type house. TNS looped through to next door. Nothing unusual there. Next doors earth is on this house's MET in 4 mm² and not the sheath of the incoming cable. Told DNO they said "We have no responsibility to supply an earth" In any event this strikes me as wrong. As far as I understand ESQCR require the DNO to maintain the earth supply in good condition.
If a fault on earth from next door goes onto this house's earth..... As this is older type wiring and various add ons over the years, there is cross bonding on water pipes etc. and supplementary bonding etc. So this house could become live on the metal work from next door earth fault. What would you say to DNO? or customer.
I'd write or email the DNO and get them to confirm thier position in writing. I suspect at that stage they will decide to rectify rather than be held to account.
 

Reply to Does DNO have to maintain/provide earth? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
992
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Evening all, I’d appreciate your opinions here: I’m looking at an old (150 years+) stone house. Complete rewire and renovation. DNO fuse is...
Replies
2
Views
3K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock