HappyHippyDad

-
Esteemed
Arms
Reaction score
5,578
The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).

Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.

I just cant see how fitting a Main Bonding cable achieves anything in this case?
 
I would say no based on niceic advice at tech talk, but I wasn't sure about that advice as the water in the copper and plastic pipes is conductive so a path to earth can penetrate.

Before anyone says anything I know pure water isn't conductive.
 
Having just watched John Ward again
I realise it does need bonding (along with what SL said above). There is the possibility (although ridiculously small) of being in contact with the stop cock and an exposed conductive part at the same time.
 
Based on your description it does not require main bonding. However if the very limited extraneous CP's are simultaneously accessible with conductive parts then I would reverse the above and bond it.
 
The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).

Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.

I just cant see how fitting a Main Bonding cable achieves anything in this case?
DRAWER mate
 
What was your first thought when you first saw this set up, what does your conscience say? My first thought was “bond it” based on your description.
 
I'm voting to bond. Plus, the Homeowner could change out the plastic at some point, just saying :rolleyes: .
 
Your own test has determined that the incoming pipe is extraneous so needs bonding as per BS7671:2018.

Whether or not it does anything or not is a mute point as BS7671 does not give much wriggle room. Is it extraneous? Yes. Is there an insulating section at the incoming point to the property? No. So it requires bonding whether we like it or not. There is nothing in BS7671 that states the main incoming water pipe needs to be accessible - 544.1.2.
 
The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).

Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.

I just cant see how fitting a Main Bonding cable achieves anything in this case?

Your own test has determined that the incoming pipe is extraneous so needs bonding as per BS7671:2018.

Whether or not it does anything or not is a mute point as BS7671 does not give much wriggle room. Is it extraneous? Yes. Is
there an insulating
section at the incoming point to the property? No. So it requires bonding whether we like it or not. There is nothing in BS7671 that states the main incoming water pipe needs to be accessible - 544.1.2.
The OP appears to state there is an insulating section close to the point of entry. Of course the stopcock will be extraneous, but the regulations clearly state now that a short section of incoming pipe which has an insulating section close to the point of entry will not require main bonding.
 
The OP appears to state there is an insulating section close to the point of entry. Of course the stopcock will be extraneous, but the regulations clearly state now that a short section of incoming pipe which has an insulating section close to the point of entry will not require main bonding.

As above- it has to be at the point of entry, not close to.
 
The OP appears to state there is an insulating section close to the point of entry. Of course the stopcock will be extraneous, but the regulations clearly state now that a short section of incoming pipe which has an insulating section close to the point of entry will not require main bonding.

Only applies if a blue plastic service pipe, does not apply if a metal service pipe!
 
I would say no based on niceic advice at tech talk, but I wasn't sure about that advice as the water in the copper and plastic pipes is conductive so a path to earth can penetrate.

Before anyone says anything I know pure water isn't conductive.

Do we get pure water out of a tap?
 

Reply to Does this require Main Bonding? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock