I think the state the shower cable had been left in - particularly at its far end - could allow N-cpc or N to 'earth/terra-firma' currents to flow depending on the potential of the N with respect to cpc or earth/t-f.

There might also be some interaction between the redundant shower cable and the lower IR reading socket circuits through the fabric of the building especially if dampness is present.

As Murdoch might have said - 'did you clamp and measure earth leakage currents before and after the changes you made'? Or ramp test the RCD before and after?

I'd also take gander and do some IR measurements on those appliances which are plugged in which could suffer earth leakage even when switched off by the functional controls eg: kettles, ovens, immersion heaters, central heating, ...or in combination accumulate a high earth leakage current.

I'd want a bit more investigation done on the low IR socket circuits. What voltage did you do the IR tests?

Thanks for the response,

I have ramp tested the RCD before and after results were mid 20's mA (Can't remember exactly) and also clamp tested the main earth which didn't show any leakage however at that exact time the RCD was not tripping.

Did the IR first at 250 and as it was low did it again with everything unplugged at 500 where I got the 2-3 MOhms readings.
 
As @marconi stated vis-a-vis the earth neutral thing, how many times have we switched off a circuit and shorted N-E and the trip trips? As the N + E were connected still to the respective bus bars...Trip! with a bit of moisture involved.

No, Never have I lopped a flex off and plunged the house into darkness, sending an irate customer into a tirade of expletives as they had lost three hours of work on their PC.

My polite suggestion they use autosave did not improve matters.

Every days an education.
 
You could connect all cores of the former shower cable to the Earth bar in the DB.

and Murdoch's #9.

I know that redundant cables are properly sealed and earthed using kits such as these when they are in the industrial, power distribution and ship setting - see:

3M Cold Shrink Cable Abandonment Kits - https://www.cablejoints.co.uk/sub-product-details/3m-hazardous-area-cable-joint-kits/cable-abandonment-3m-cold-shrink-cscak

I don't know what the rules and regulations say about the redundant cables in the domestic/office setting. I think it odd though to not completely disconnect, isolate and label up such cables (including cpc and armouring) in the domestic/office setting (eg the shower cable in this post) so that such cables are safely made no longer part of the electrical wiring and thereby cannot play any further part in the flow of any currents in that installation.
 
Last edited:
Customer called nuisance tripping every night approx 10:30 ish this week in a very large house and outbuildings.
Ramp tests fine. Had a low IR 0.23 meg (250v) reading with everything plugged in, tracing through 4x DB's to get to the main N-E cause which served 2x outside lights in a remote barn. Disconnected them and investigated another DB which the RCD had also tripped once for the underfloor heating, IR fine but MCBs were very loose on busbar. At 1.22M ohms (@250V) on the main DB (NOT unplugging anything) I left happy things were much better but played the cautious card. Customer called to say the last 2 nights were fine. Sometimes you simply cannot reasonably isolate all electrical items connected that give you a very low reading to find the faults as quick as possible. 3 hours later and god knows how many steps including a bit of jogging keeps one fit along with the mental exercise !!
 

Reply to Domestic favour, tripping RCD and redundant circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
963
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock