Guys

don't have my big read book handy at mo can you answer the following

1. 32amp circuit were protective measure against electric shock is ads is the maximum disconnection time permitted by bs 7671 = 0.5s

2. maximum Zs permitted by bs7671 for a 32amp circuit

3. What is the bs(en) for a rcd domestic


cheers
 
Q1. Don;t understand the question!

Q2. Depends on type of protective device.

Q3.

BS 3036 Rewireable Fuses
BS 1361 Cartridge Fuses (Consumer Unit Type)
BS 1363 Plug Top Fuses
BS 88 Cartridge Fuses (General purpose)
BS EN 60898 Miniature Circuit Breakers
BS 3871 Miniature Circuit Breaker (Old Style)
BS EN 60947 3 Main Isolators
BS EN 61008 Main RCDs
BS EN 61009 1 RCB0s
BS 7288 RCD Sockets
BS 1363 13A Plug Tops
:D
 
32amp and above is 5.0 secs, 0.4 for anything below
Max Zs for type b 32 amp is 1.16 ohm.........already adjusted to 80%of 7671
 
32amp and above is 5.0 secs, 0.4 for anything below
Max Zs for type b 32 amp is 1.16 ohm.........already adjusted to 80%of 7671

Let me correct you slightly...

All final circuits rated 32A or under - disconnection time of 0.4s.
All distribution circuits and all final circuits OVER 32A - disconnection time of 5s.

And as stated above Max Zs for a tybe b MCB rated at 32A is 1.16 ohms(already with the 0.8 correction factor calculated).

Hope this makes things clearer for you

Cheers
 
Last edited:
Guys

don't have my big read book handy at mo can you answer the following

1. 32amp circuit were protective measure against electric shock is ads is the maximum disconnection time permitted by bs 7671 = 0.5s

2. maximum Zs permitted by bs7671 for a 32amp circuit

3. What is the bs(en) for a rcd domestic


cheers

1. dis time 0.4s
2.zs max 1.44 ohms
3.bsen 61009
 

Reply to Domestic in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
hi all, Got a question that i am not understanding correctly? Any body know how to work this out, I thought the answer was D, but apparently its...
Replies
4
Views
1K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock