Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
obviously wago'd into the other cpc where ther are 2 cables?????
 
Click Flow connectors.

And how would it be connected to the Earthing arrangement if there is more than one luminaire?
Doesn't look like there is enough room in those fittings for loop in/out and switch so assuming that is done in a JB.

Otherwise you're right, the CPC needs continuing.
 
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
If we have the same situation in mind then yes.

That is single feed to a single luminaire, all other cables terminated elsewhere; click distribution box, lighting JB or similar.
 
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
Not wanting to start WW3 but, what requirement is there to enclose a CPC?

526.5-8 specifically refers to live conductors.

Am I missing something?
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
 
As the cpc has been removed from the cable sheath which affords it protection then 521.10.1 would apply.
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
What do you suppose cpc stands for.
 
I'd still contend, that in the case of a CPC feeding a single luminaire, that it is not a "protective conductor" as the CPC is not linking Exposed Conductive Parts, if it were the CPC would be connected to the accessory, and therefore there is no requirement to enclose.
 
What do you suppose cpc stands for.
There are protective conductors and Protective Conductors.

Other than the instance highlighted above the CPC does not fit the definition on P33 and is not specifically listed as an example.

It is their for fault protection not electric shock protection.

So, as i read it, a CPC can be but is not always a protective conductor.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
On two occasions recently when changing light fittings I've been bored enough (after fitting the light naturally), to read the instructions that...
Replies
4
Views
2K
UK 2022 based regs question. Hello, I have a new extension and the builders electrician has required much of the house ( not asked for ) and...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock