21.10.1 Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking. This requirement does not apply to a protective conductor complying with Section 543.......
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
Nothing says the whole of the CPC has to form part of a multi core cable.
That wouldn’t be possible even if the termination was within an enclosure.
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
Quite correct but your words are going to deaf ears.
 
Quite correct but your words are going to deaf ears.
I think if anyone has deaf ears, it’s you.
You cite a Regulation which does not apply, then despite me quoting the Regulation which clearly states it does not apply, you then go right back and cite the Regulation again.

Like I said, find a Regulation that requires a CPC that forms part of a multi core cable to have a minimum CSA and find another that requires terminations to be enclosed.
Once you’ve found (or think you’ve found) those Regulations, then explain how they apply to main bonding and earth conductors.
 
Well if minimum CSA is not an issue, why are you agreeing with Wilko?
How is it earthing and bonding conductors can be terminated without enclosures, but the CPC in this instance can’t?
It's obvious even without a regs book mechanical protection of the conductor especially small conductors of that size.
 
When have I quoted minimum csa, as I say I have no idea where you are trying to take this.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
On two occasions recently when changing light fittings I've been bored enough (after fitting the light naturally), to read the instructions that...
Replies
4
Views
2K
UK 2022 based regs question. Hello, I have a new extension and the builders electrician has required much of the house ( not asked for ) and...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock