Discuss Double oven and hob problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Mike22

-
Reaction score
2
My mum is wanting to have 2 ovens (2.9kw) and an induction hob (2.8kw) total 8.6kw I believe all 3 are coming with 13a plugs fitted.
What would the best way to connect these up?
Existing wiring which is 6mm t+e approx 6m under floorboards.
I was thinking like the dual outlet for cookers do they do a triple, or would it be best fitting sockets in 6mm (if a socket can take 2x 6mm cable)?
 
you could use 6.0mm cable to 45A cooker isolator, and on to a cooker outlet. from there take 3 x 2.5mm, 1 to each socket
 
R u sure the induction hob is 2.8 kW? It doesn't seem enough.
Saying that, even if it is 6kw with diversity it may still be OK.
If it's 7kw it may not be.

According to the website that it has been purchased from, does it seem a bit too low? I've never used or even seen an induction other than in pictures, can't bebe gas!
 

Reply to Double oven and hob problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
196
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi All, An easy one for you guys I expect... I have 6mm² to kitchen, RCD protected, B32. I need to provide supply to an oven, hob (ignition...
Replies
4
Views
1K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock