New kitchen install
Integrated Double oven unit
Integrated single oven unit
Next to each other
Existing circuit
6mm 32A mcb
New double oven manufacturers instruction
40A fuse hard wired
New single oven manufacturers instruction
16A fuse hard wired
Existing cable too short for new isolator position, needs to come out and be replaced
So
According to manufacturers instructions
I need 10mm cable (for the 40A fuse) regardless of diversity
Anyone come across this and do you abide by manufacturers instructions or do you diversity and cable calc to size cable
So two dedicated circuits to two isolator
Then how to route cables to ccu
Do you go down below worktop and the over and up to ccu or space permitting go horizontal through one of the isolators
Or is there a neat way for two isolators to two ccu
Any Recommendations on best way of connection
Do I include the option for if the single oven gets upgraded to another double oven
Not bothered about hob as this is going in island on another dedicated circuit
Any advice greatly received
Many thanks for looking
Integrated Double oven unit
Integrated single oven unit
Next to each other
Existing circuit
6mm 32A mcb
New double oven manufacturers instruction
40A fuse hard wired
New single oven manufacturers instruction
16A fuse hard wired
Existing cable too short for new isolator position, needs to come out and be replaced
So
According to manufacturers instructions
I need 10mm cable (for the 40A fuse) regardless of diversity
Anyone come across this and do you abide by manufacturers instructions or do you diversity and cable calc to size cable
So two dedicated circuits to two isolator
Then how to route cables to ccu
Do you go down below worktop and the over and up to ccu or space permitting go horizontal through one of the isolators
Or is there a neat way for two isolators to two ccu
Any Recommendations on best way of connection
Do I include the option for if the single oven gets upgraded to another double oven
Not bothered about hob as this is going in island on another dedicated circuit
Any advice greatly received
Many thanks for looking