Rod Hubbard

I have these downlights installed under loft insulation with halogen GU10s. They are marked as fire rated and fire rated under insulation, but the installation just doesn’t look safe? I’m wondering if i should convert them to LED bulbs (that's happening progressively as the halogens blow anyway) and put plastic cage covers, the SpotClip type, over them and better meet building regs?

Downlight2.JPG
 
as above. but get them halogens out. replace with GU10 leds. the closeness to the joist/s will not be a major issue then. and do not cover with itchy snot.
 
By all means change the GU10's to LED's BUT LED's will get hot too , so you need to prevent the insulation from covering the lamp.

As others have said they are too close to the joists!
 
There's a fire waiting to happen as said these halogen GU10 can have a temperature of 200 degrees put next to a dry wooden truss. I remember in my previous employment as a Q.S. seeing a fire rated downlight drilled into a joist electrician said to me well the light is fire rated ,yes it will prevent the spread of fire through the hole but it is more likely to start it said it all really.change it to LED GU10 and fit a loft box over.
 
UK's love of downlights carries with it a very significant carbon footprint.
Get them covered, but only if Led and then ideally only if insulation coverable ones. There are some integrated type which are specified for use that way, otherwise check out Icage for GU10.
 

Reply to Downlights and Loft Insulation in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
264
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hello, I wish to purchase some Downlights to replace some halogen spotlights in my bathroom. Currently the existing spotlights are powered through...
Replies
8
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
154
I am installing 9 LED downlights each with an RGB bulb in (i will try attach pictures on them) - anyway I have been told that they need to be...
Replies
4
Views
739

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock