    Dear All
    Got a board change to do where there is an incoming oil pipe.
    Plastic tank with PVC covered copper pipe most of the way. Comes inside and its just copper coming up through the floor. Did an IR test and got 0.00 so it needs bonding ( as I understand it its got to be under 0.02 to not need bonding)
    Problem is the pipe is only about 8 or 9 mm dia. and i cant find a small enough clamp.
    Someone suggested either a P clip or strap banding but they dont seem very professional. what are people using please
    cheers
    dnjr
     
  2. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You can get Ezybond clamps but they only go down to 15mm from what I have seen. There are rumours these are not in compliance with BS951 but I believe the manufacturer has resolved this.
     
  3. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    Hi Westward. Yep seen them but as you say dont go small enough. I cant be the only person needing to bond oil pipes. there must be something out there....
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    bare copper p-clip is the answer. 4mm brass nut & bolt with a lug on the bonding cable.
     
    • Like Like x 2
  5. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
  6. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you can't over tighten them things. the bolt will shear before it crushes spaghetti.
     
    • Agree Agree x 1
    • Funny Funny x 1
  7. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    You might want to check your maths there!
     
    • Agree Agree x 3
    • Like Like x 1
  8. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    teach me to read first
    IR was 0.00M ( as I understand it , if its below 0.02M then it needs bonding if its above 0.02M then no need. Think I meant to put Over 0,02 but typed under...
    Am I right this time davesparks ?
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    over 0.22Meg means it's not extraneous and does not need bonding. if under that, a continuity test is required from pipe to MET. a reading below 1.0 ohms suggests that it is bonded through other services, e.g.water and may not need additional bonding.
     
    • Like Like x 1
  10. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    Hi Teletrix
    I thought it was 0.022M ( 22000 ohms)
    over that dont bond under that and it needs bonding
    I did a continuity test and got 0.06 ohms I had it in mind it had to be below 0.05 to be acceptable (GN3) could be wrong, its been a long day
    I cant find either a oil pipe bond or a water pipe bond so getting worried and going belt and braces
     
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    that 0.05 figure has to be the most misquoted figure of all time. it's the max. resistance betweem a bonding cable and the pipe to which it is bonded. I.E the resistance across the bonding clamp from cable to pipe.
     
    • Like Like x 3
    • Agree Agree x 2
    • Winner Winner x 2
  12. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Precisely. It's just to demonstrate that the clamp is adequately connected to the pipe!
     
    • Agree Agree x 4
  13. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Also including some clue as to the units is quite important, I didn't quite register that you used an IR tester and was thinking in ohms.

    My opinion on this subject is not exactly in line with the popular opinion on the forum, I'm inclined to interpret the regulations as requiring incoming services that be bonded at point of entry.
     
    • Like Like x 1
  14. sparkdog
    Offline

    sparkdog sparkdog Electrician's Arms

    Location:
    Sunny Sussex
    Business Name:
    C MacRae Electrical
    I usually manage to fit a standard earth clamp to an oil pipe.
     
    • Agree Agree x 2
  15. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    I've tried. Just too big for this one.
     
  16. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    I did that once on a 10mm PVC coated soft copper oil pipe and crushed it, apparently the plumber thought this was a bad thing, but I just told him it was revenge.
     
    • Like Like x 1
  17. suffolkspark
    Offline

    suffolkspark Electrician's Arms

    Location:
    suffolk
    I've only been in the trade 14 years which know isn't as many as some on here, but I've never had an issue doing this either? I've always used Tenby ones I know some cheaper ones are a different shape so perhaps don't grip smaller things?
     
    • Agree Agree x 1
  18. sparkdog
    Offline

    sparkdog sparkdog Electrician's Arms

    Location:
    Sunny Sussex
    Business Name:
    C MacRae Electrical
    MICC Pyro bare copper P clip as mentioned earlier.
     
  19. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    thanks all. Will try p clips
     
  20. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    Wholesaler came up with this
    It's an earth bond link made by Tamlex for trunking bent round. Giving it a go
    V__2E10.jpg
     
    • Like Like x 1
  21. suffolkspark
    Offline

    suffolkspark Electrician's Arms

    Location:
    suffolk
    I still di t get why an earth clamp wont fit? Take a pic im intrigued, ps dont forget to affix bonding label to your clamp
     
  22. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    Hi Suffolk
    Standard clamps I have seen either have a sort of box section bit in the clamp which would wobble about on top of the pipe or have a 'U' shaped but with the clamp which is too big and straddles the pipe and band can't go tight enough. Honest. I've tried. ...
     
  23. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    wind a bit of bare 6.0mm round the pipe. solder in place. sleeve the tail after .
     
    • Like Like x 1
  24. dnjr
    Offline

    dnjr Regular EF Member

    Location:
    South coast
    Now that is a bloody good idea
    Hats off to you
     
  25. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Some care required if you are planning to solder a heating oil supply line. From memory, soldering needs about 200C and the auto ignition point of heating oil is about that too. Just saying ...
     
    • Like Like x 1
  26. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    1.do it when there's no oil in the pipe

    2. clamp heat sinks on pipe to prevent the oil overheating. it needs to vaporise to ignite.
     
  27. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    The oil will not ignite unless it reaches temperature where it vaporizes allowing it to mix with oxygen, liquids do not burn it will however act as a heat sink removing the temperature from the pipe.
     
    • Agree Agree x 1
  28. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    That's right, these fuels won't burn without air. It's my understanding the vapour point of heating oil is significantly below the melting point of solder. Again, just saying ...
     
  29. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    maybe an experiment.... a whole new concept of the bang test.
     
    • Funny Funny x 1
  30. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    The flash point of heating oil depending on the type will be approximately half 200°C.
     
  31. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    but how can it vaporise when it's confined in the tube?
     
  32. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Witchcraft
     
    • Funny Funny x 1
  33. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    It can expand but even if it did manage to reach flash point and vaporize it would still need a sufficient heat source to ignite. Highly unlikely but most things are possible especially if it started spraying from a joint due to the expansion. I personally would not try it.
     
  34. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I'm not saying death and destruction will ensue, but I would "prudently avoid the known risk" of applying heat to a fuel line.
     
    • Agree Agree x 2
  35. Guitarist
    Offline

    Guitarist Trusted Advisor

    Location:
    Norfolk
    I've never had an issue getting standard earth clamps to fit a 10mm oil pipe.
     
  36. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    I've used a length of 1.0mm bare copper before. Bind it in tight turns around the pipe and back on itself if necessary. Clamp over that, done right it'll fit tight.
     