Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Earth bond to external oil boiler.... in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    External oil boiler, (just outside kitchen) oil pipe buried through garden to tank. Plumber says it doesnt need bonding as its outside? Am i missing something?? Copper pipes entering house from boiler.
    Thoughts
     
  2. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Sounds like one of the ‘examples’ given in BS7671, that requires bonding.
     
  3. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - guessing the boiler will be earthed via cpc, but any pipe entering the house may need bonding I'd have thought. Perhaps confirm installation instructions whether the external boiler, external oil tank and pipework needs any special treatment. Maybe Mr Plumber's done that?
     
    Last edited: Jan 10, 2019
  4. Bellendian
    Offline

    Bellendian Regular EF Member

    Location:
    Gatwick
    The oil pipe won't if it doesn't enter the building. The ch primaries are likely to need bonding where they enter the building if they are metallic.
     
    • Agree Agree x 3
  5. cliffed
    Offline

    cliffed Regular EF Member

    Location:
    Lancs
    The last one I did the oil pipe was plastic,but if it’s metal & enters the house then it needs to be bonded.
    Just like back in the good old days.
     
  6. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    Don't listen to a plumber!!
    As above, incoming metallic pipework that is extraneous will need bonding at the point of entry
     
    • Like Like x 2
  7. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I've altered that, like some do; I'd argue it needs bonding no matter what they say, in a non Boyszone Kim way.
     
  8. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    Well the regulations only require the bonding of extraneous conductive parts, you are welcome to waste your time and customers money, I'll stick to the requirements! :)
     
    • Funny Funny x 1
  9. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    I agree if the pipes entering the property from the boiler are also copper then this is bringing an extraneous conductive part into the installation and requires a main equipotential bond.
    I though that pipes had to be copper within 3 meters of a boiler but could be very wrong on that?!
     
  10. Bellendian
    Offline

    Bellendian Regular EF Member

    Location:
    Gatwick
    Think it's normally 1m, but don't quote me on that. At the end of the day it's down to the MI's for each boiler.
    To an extent, you don't care. If water clown has used plastic then no bond, if it's metallic then bond it.
     
    • Agree Agree x 1
  11. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Testing, testing. All I would say then, over the course of time, a lot of people have had their time & money wasted.
     
  12. DNO
    Offline

    DNO Active EF Member

    The PME requirements are that the tank/pipework (external) is staked down. Internally, as always a bond is fixed on the consumer side of the tap and any insulated insert. This has nothing to do with wiring regulations which are non mandatory.
     
Loading...
Similar Threads - Earth bond external Forum Date
Main earthing Conductor also bonds water Electrical Forum Tuesday at 5:53 PM
Should a giant steel framed human aquarium be earth bonded? Electrical Forum Oct 25, 2018

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job