Discuss Earth Fault Loop High ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

acestu

Hi, I have just purchased the martindale socket tester EZ150 which gives me an earth fault loop reading, now i plugged it into the sockets in my mates stables and the green light in the middle came on instead of the first green light, would i be right in thinking that if i have a 32 amp breaker feeding the sockets then the EFLI should not be above 1.44 ohms if so the middle green light 1.7 - 5 ohms is high, do i need to investigate this.

The stables are fed from a three core armoured and the house is about 200 feet away, i have been taught that you should not export the earthing system, so should i devorce the earth at the stable end and put an earth rod in ?

cheers
Acestu
 
Hi, I have just purchased the martindale socket tester EZ150 which gives me an earth fault loop reading, now i plugged it into the sockets in my mates stables and the green light in the middle came on instead of the first green light, would i be right in thinking that if i have a 32 amp breaker feeding the sockets then the EFLI should not be above 1.44 ohms if so the middle green light 1.7 - 5 ohms is high, do i need to investigate this.

The stables are fed from a three core armoured and the house is about 200 feet away, i have been taught that you should not export the earthing system, so should i devorce the earth at the stable end and put an earth rod in ?

cheers
Acestu

Get a proper EFLI tester and not a mickey mouse lights gadget.
 
it may be worth getting it investigated with a calibrated tester. I think that the tester you have is really just a rough indicator. but if i were you i would def get it looked at. You are looking for advice, which is what this site is for. I dont know why the person who answered above me has to answer in such a rude way, there is no need for it. If people cant be civilised, why contribute ?
 
I will be getting an all in 1 shortly as i have just past my exams...

Not really what i wanted to hear though, hope there are more helpful people on here

I love forums there always somebody like you

Acestu
 
Thanks guys im not stupid i should of said that it was just a rough test which is now leading me to investigate further with proper equipment, the socket tester is a great 10 second test which can alert you to further investigation, what i really wanted was input on the rest of the question, i know you all think im just another punter fekin about with electric when he shouldnt be, but im a time served spark and i have just done 17th edition and 2391 also pat testing and pat testing management so is there any chance of a bit of friendly advice or not

thanks
Acestu
 
If you have taken these course then you should be using the proper test equipment and not relying on a mickey mouse bit of kit
 
no one is trying to imply anything mate. we have to assume that you have no knowledge, so that we dont mislead people. If somebody who isnt trained reads this, and we advocated the use of your EFLI indication device, then they might think that they could substitute a full test with that. this forum really is helpful to experienced blokes and to trainees alike. nobody knows everything.

Hope you enjoy this site

John
 
I am having real problems getting through to people on here , i will be using proper kit to test now that i have been alerted to the problem, it wasnt an inspection and test or anything until my friend pluged in my tester in the socket, i just wanted peoples advice on the earthing system

Acestu
 
How is the earth exported?
Is it by the armour of the SWA, or through a core of the cable?
If you do divorce the earth at the stable and install a rod, unless you can get the impedance of the rod down low enough you will have to install an RCD to comply with disconnection times.
Some would consider that installing an RCD will allow you to get away with high Zs, without making the stable TT, I believe up to 1667 if using a 30mA RCD.
 
Last edited by a moderator:
have you checked the cable calcs? if the house is a long way away, then cable may be undersized, giving rise to high Zs. You could reduce the size of the MCB protecting the circuit, and that will allow you some flexibilty, providing all calcs hold up.
 
you are correct in saying that the Max zs should be 1.44 however the maximum tested value should be 80% of that which is about 1.15 so anything higher than that should be investigated
 
I guess it depends how you define an agricultural building.
In Cambridgshire the Local Authority do not consider stables to be agricultural, and they require planning permission and if sited on agricultural land a change of use application.
 
Finally a bit of a debate on special locations and earthing arrangments,

I was taught that different electrical supply companies have different rules on exporting the incoming earthing system, and that rule of thumb is that if the outbuilding cannot be touched from the main building then an earth rod should be used and a TT system used, what are your thoughts on this....

Interesting bit on stables as agracultural buildings...

Thanks
Acestu
 
There's nothing in BS7671 preventing the exportation of an earth.
The main problem is the DNOs. Where the supply is PME, you should ask their permission before exporting.
Also if there are any extraneous-conductive-parts that require bonding, you will have to supply an appropriatly sized conductor. The armour of the SWA will not be sufficient.
 
Special locations ,stables are Part of agricultural buildings and special locations section 705 of the regs ,and the reason is horses can be classed as live stock its an animal so it is required to be protected against electric shock and burns etc also stables contain flammable and combustable materials IE straw and hay , also the cleaning methods in stables are water jets so it will then require accessories to be IP rated to IPX5 , cabling should be protected against damage which in general terms will be SWA as steel conduit rusts , as for a question the swa although you can use the armour as an earth, but it would be far more benificial to use a cable with an incorperated earth as some sizes you will require an additional earth
 
Last edited by a moderator:

Reply to Earth Fault Loop High ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
659
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I have a Martindale EZ165 and have used it previously to do basic earth loop test on sockets in the UK. I want to carry out the same...
Replies
1
Views
1K
Hi. We have a circuit where some of the sockets have a dangerously high earth loop impedance. This was identified by a professional electrician. I...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock