As can be seen from my profile I am not a qualified electrician but I'm studying in my own time just for the sake of it. I understand the principals of earthing and bonding but in this video by GSH Electrical....


.....at 2:10 minutes in he says exposed conductive parts under earth fault would have "up to 50 V appearing"....can someone explain how he gets 50 V please .....I'd have thought it'd be instantaneously 240 V before ADS
 
Or, phrased another way, ADS is designed so that any fault that could create a potential of 50V or more between exposed conductive parts, must cause a protective device to operate. The 50V is a designed-in limit.
 
Just for fun - check out 3:50 where chap states the limit for bonding conductor resistance is 0.05 Ohms. As far as I'm aware this is not so - it's an indicator of a good connection rather than a hard limit (from GN3 p38). So there is no need to exceed the sizing requirements in BS7671. What do you think ?
 
Just for fun - check out 3:50 where chap states the limit for bonding conductor resistance is 0.05 Ohms. As far as I'm aware this is not so - it's an indicator of a good connection rather than a hard limit (from GN3 p38). So there is no need to exceed the sizing requirements in BS7671. What do you think ?
You are correct wilko.
It’s a figure that many take to be gospel yet they quote GN3 which has neve actually said this.
In fact the latest GN3 18th edition version actually goes onto say that a 0.05 ohms reading is not from the MET to the pipework or bonding conductor in question
 
Thank you all for your replies, you pointed me in the right direction and I found this....

"The maximum value is R = 50/Ia. Where Ia is the operating current for the protective device in 5 seconds. Ref. 413 - 02 -28. GN3 recommends less than 0.05 ohms."..

.
...it might not be bang up to date but I understand the principle now.... ....Ia being the pfc?
 
You are correct wilko.
It’s a figure that many take to be gospel yet they quote GN3 which has neve actually said this.
In fact the latest GN3 18th edition version actually goes onto say that a 0.05 ohms reading is not from the MET to the pipework or bonding conductor in question
Oh dear, this means I will just have to get a new GN3 :rolleyes: ...
 
the 0.05 ohms figure is for the resistance between the bonding cable end and the pipe to which it is connected. i.e. to verify that the bonding clamp is securely connected to the pipework metal. nothing to do with the resistance of the cable.
 
Thank you all for your replies, you pointed me in the right direction and I found this....

"The maximum value is R = 50/Ia. Where Ia is the operating current for the protective device in 5 seconds. Ref. 413 - 02 -28. GN3 recommends less than 0.05 ohms."..

.
...it might not be bang up to date but I understand the principle now.... ....Ia being the pfc?
R=50/Ia

For example if you had no rcd protection in a bathroom and you wanted to verify the effectiveness of the supplementary bonding.
Lighting circuit protected by a 6amp type B circuit breaker
Then it would be R=50/30=1.67 ohms.
If it was a type C 6amp mcb then it’s 50/60=0.83 ohms.
That is the maximum resistance between pipework before any fault current in the location between exposed and extraneous parts exceeds 50v.
The 0.05 figure is a red herring.
It’s for measuring between pipework where the clamps are hidden or ‘built in’
A 0.05 ohms reading between pipework verifies that there’s little resistance between said pipework
 
Last edited:

Reply to Earth fault - potential on exposed conductive part in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just watched one of John Ward's interesting videos - It all makes sense apart from one of the final points involving adding an earth rod...
Replies
24
Views
4K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
Firstly, this chap seems very professional and I like his (plethora) of videos. It is just to discuss one aspect of his work in the one video. I'd...
Replies
4
Views
2K
Ok so I'm finishing off some questions for a mock exam and its come up with: "Explain why an exposed-conductive part MUST be connected to the MET...
Replies
11
Views
2K
Hi all, Hoping for a little advice. I work in the Asbestos industry and we manufacture mobile decontamination units we follow the HSE 247 that...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock