Called out today by new owners to a domestic 3 bed semi with history of nuisance RCD tripping from day 1 (lived there about a month). TNS. No dual supply. No regular pattern to tripping. Most appliances new.

First - Ramp Tested RCD unit with no loads = 25mA (can live with that). Popped leakage tester on earthing conductor =0.2A (yes AMP!). Opened MCBs one by one - no change - finally main incomer - but still 0.2A (see photo). Any thoughts? (please ignore the obvious other errors on the board).

Earth Leakage.JPG
 
Visible TNS connection looks good (visible bit anyway). Disconnected EC from CU end and zero reading. Measured 0.1A on bonding conductor to gas though. Water not tested yet. Haven't carried out Ze yet (ran out of time) but will do on next visit.

Never experienced before on a domestic - I'm wondering if there's leakage from DNO running through from supply sheath to gas/water pipes via bonding? Or am i on the wrong track completely?
 
What are the RCD tripping times like?

Occasional nuisance tripping is a pain! I normally ask the homeowner to keep a diary of when it happens....... to see if there is any pattern - sure they say no regular pattern but by making notes they may spot something.

Had a case recently where the "pattern" was when the misses got home - and plugged in her laptop charger!
 
Visible TNS connection looks good (visible bit anyway). Disconnected EC from CU end and zero reading. Measured 0.1A on bonding conductor to gas though. Water not tested yet. Haven't carried out Ze yet (ran out of time) but will do on next visit.

Never experienced before on a domestic - I'm wondering if there's leakage from DNO running through from supply sheath to gas/water pipes via bonding? Or am i on the wrong track completely?
You might be onto some thing with that last comment, your getting 0.2amp, but which way is it flowing?
 
If I understand correctly, you have isolated the installation at the lovely Protek iso and you are still seeing 0.2A on the earthing conductor? So there must be a voltage on the DNO means of earthing that's causing the current flow. Possible poor earth at local transformer and your installation's bonding looks better ?
 
As above clamp the live and neutral tails
clamp round the line and neutral conductors only (Not the protective conductor) and will measure the difference between the line and neutral currents, which is the earth leakage.
 
How far from the substation is the property? The reason I ask is that I've seen this before where there's possibly a ground fault current on the dno's network probably from the hv side of the tx. Try isolate the cu and check if there's still leakage if there is then you have the same problem as I've got, I even get leakage of approx 700mA (which fluctuates) when the whole area is down on the lv side during a power outage! The dno have been informed about it and are next to useless as they'll only check Ze and measure the input voltage.
 
Although the installation presents as TNS, chances are that the DNO will have created N-E bonds elsewhere on the supply network during repairs. Ze test may show similar figures on L/E & L/N tests. Small diverted neutral current on main earth is not that unusual in TNC-S.
 
Last edited:
When removing items from sockets, seeing the insulated earth pin of the TV, my first thoughts were, it wont be that causing leakage - forgetting that an aerial lead was in use and connected to a loft amplifier.
Never too old to learn.
 
this thread is getting too serious. time to chill.
 

Reply to Earth leakage - no load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Quite old main switch RCD, it occasionally trips (every day or two), then won't turn on until all breakers are off. Ramp test at time of testing...
Replies
40
Views
4K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock