    Location:
    marlow
    My house has a PME earth system. The gas pipe in the garage has a 6mm earth wire already but I've been told this should be changed to 10mm.I'm having an EV charging point fitted externally which required an earth rod to be installed (32ohms impedance measured)-PME cannot be used with an external EV charging point. Would it be acceptable to disconnect the 6mm PME earth from the gas pipe and connect the 10mm cable to the EVSE earth rod?
     
  2. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    is the garage separate from the house !
     
  3. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    If the GAS pipe in your garage is the incoming feed to your house, then you need to BOND it to the MET which will be at the entry point of the Electric cable and meter, you are not earthing the gas pipe you are bonding it to earth
     
  4. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    No
     
  5. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    No. It'll be a bonding conductor (not an earth wire), which needs to be connected to the main earthing terminal near the incoming electrical supply, not a separate rod.
     
  6. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    I would say no on the basis the existing 6mm is running to the house CU / MET and the advice you have is that this needs to be upgraded to 10mm - back to the CU / MET.
     
  7. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Make the entire garage TT bond the gas in the garage to the TT system. The EVC point can then be connected to the TT system. Run a seperate 10mm bond from TNCS MET In the house to point of entry of the gas to the house. Assuming garage has own board and RCD.

    Edit: ignore this as I assumed it was detached from the house.
     
    Last edited: Aug 11, 2017
  8. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    what's the betting the garage is attached to the house!
     
    • Like Like x 1
  9. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    lol....I must admit I had assumed it was detached.
     
  10. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    I think the clue is in the thread title...
     
    • Funny Funny x 2
  11. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    remember playhouse ,is it a round window or square window!
     
    • Like Like x 1
  12. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi Phil - let me paraphrase a sentance from the EV charging Code of Practice section 6.6 "when an EV charging point is supplied from a dwelling with PME, earthing and bonding require careful consideration". Then there's the EV section 722 in BS7671, another riveting read, no doubt.

    It sounds like your gas bonding was not up to scratch from a change to PME and so that just needs to happen. The design of the EV system is another thing, imho :)
     
    • Like Like x 1
    • Agree Agree x 1
    Last edited: Aug 11, 2017
  13. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    oops :oops:
     
    • Funny Funny x 1
  14. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    upload_2017-8-11_17-51-0.png we will have to wait on this one!
     
  15. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    these threads are getting slower ever day we need to have count down clock.
     
    • Funny Funny x 3
  16. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    tick tock. mouse ran up the clock.
    got his pants caught in the works
    paralysed his cock.
     
    • Funny Funny x 4
  17. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    Oh, that's why you are 'top poster of the month' - still beats the drivel that westy used to come out with though!
     
    • Funny Funny x 1
  18. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Would you like to enlighten me with examples of this drivel.
     
    • Funny Funny x 1
  19. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    Sorry westy. Just trying to make Tel feel better about being 'top poster of the month' not everyone can handle the responsibility whereas YOU, now you excel at being TPOTM.
     
  20. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Top Poster way out of reach now.
     
  21. Dave OCD
    Offline

    Dave OCD Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    Playschool not Playhouse ya silly ar5e and it was round, square or arched window. :D
     
    • Funny Funny x 3
    • Like Like x 1
  22. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    More important things going on?
     
  23. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    @RSE@RSE is a member - how funny is that! Or unfortunate however you look at it!
     
    • Like Like x 1
  24. Andy-1960
    Offline

    Andy-1960 Electrician's Arms

    Location:
    Wolverhampton
    The clue is in the title of the thread!!!
     
    • Like Like x 1
  25. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    I'm so detached I don't care
     
    • Like Like x 3
    • Funny Funny x 1
  26. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    she was only the welder's daughter, but she had acetylene legs.
     
    • Like Like x 1
    • Funny Funny x 1
    • Winner Winner x 1
  27. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    Gettin slow Tel a set of lean legs, message to myself, leave that bleedin wine alone took me 3 mins to understand what you meant, or is it Alzheimers?
     
    • Funny Funny x 1
  28. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You see.
     
  29. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    I get ya!
    But I don't feel ya!
     
    • Like Like x 1
  30. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    I need my night time meds
     
    • Like Like x 1
    • Funny Funny x 1
  31. Dave OCD
    Offline

    Dave OCD Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    The version I'm familiar with ends higher up than legs.:D

     
  32. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Glad you do, as I clearly need more red to keep up here ...
     
  33. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    That's filthy, well last time I looked it was:p
     
    • Funny Funny x 3
  34. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    ...Well just run a damp flannel over it...and continue ;)
     
    • Funny Funny x 3
  35. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    farmer goes out into his cow field @ 5 o'clock on a bitter winter morning. cows are all lying down, frozen stiff, no life at all. panicking the farmer is lost for what to do when an old lady walks by.

    she says to the farmer "what seems to be the matter?"
    farmer replies "All my cows are dead, frozen stiff"

    walking over to the first cow, the old lady breathes into it's nose. She repeats this with all 200 cows.

    Slowly but surely, all the cows recover and walk towards the field gate, heading for the milking shed.

    "Bloody 'ell" says the farmer. " I must pay you for saving all my cows"

    "No need" she replies.

    "Well, what's your name , so I can sing your praises around the village" says the farmer

    "Thora Hird" she replies.
     
    • Funny Funny x 3
  36. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    Not one of those buttons described how I felt when I finished reading that joke!
    We need one that groans!
     
    • Like Like x 2
    • Funny Funny x 1
  37. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I have just quickly read threw this thread before I retire and get the feeling that none of you can actually answer the OP's question, nor can I. Lets see what tomorrow brings
     
    • Agree Agree x 1
  38. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you retiring mid? didn't think you were that old.
     
    • Funny Funny x 1
  39. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I don't have a mid afternoon nap like you do :)
     
  40. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    (gentle cough) ... Pete says no with reasons back in post #3 ...

    It's even more no with the EV charging point that's in play. There are couple of ways to proceed with a domestic EV design with PME at the house, and one of them (at least) would be busted with the OP proposal.
     
  41. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire

    Is the gas pipe metal or extraneous, can see that in any of the OP's posts?
     
  42. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Haven't the foggiest about EVCI, but I do see that reg 722.411.4.1 is so ambiguous as regards PME, that the grown ups have decided to clean it up a bit with the forthcoming 18th.
     
  43. PhilCapron
    Offline

    PhilCapron New EF Member

    Location:
    marlow
    The gas pipe is metal and the garage is attached.
    HTH.
    Phillip Capron.
     
  44. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    As I suspected.

    The gas bonding needs to be upgraded to 10mm back to the fuseboard or MET.....
     
  45. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    hum.... many of our regs are ambiguous.........................

    Still want them to add a definition of "accessible" to the regs.
     