My house has a PME earth system. The gas pipe in the garage has a 6mm earth wire already but I've been told this should be changed to 10mm.I'm having an EV charging point fitted externally which required an earth rod to be installed (32ohms impedance measured)-PME cannot be used with an external EV charging point. Would it be acceptable to disconnect the 6mm PME earth from the gas pipe and connect the 10mm cable to the EVSE earth rod?
 
My house has a PME earth system. The gas pipe in the garage has a 6mm earth wire already but I've been told this should be changed to 10mm.I'm having an EV charging point fitted externally which required an earth rod to be installed (32ohms impedance measured)-PME cannot be used with an external EV charging point. Would it be acceptable to disconnect the 6mm PME earth from the gas pipe and connect the 10mm cable to the EVSE earth rod?
If the GAS pipe in your garage is the incoming feed to your house, then you need to BOND it to the MET which will be at the entry point of the Electric cable and meter, you are not earthing the gas pipe you are bonding it to earth
 
My house has a PME earth system. The gas pipe in the garage has a 6mm earth wire already but I've been told this should be changed to 10mm.I'm having an EV charging point fitted externally which required an earth rod to be installed (32ohms impedance measured)-PME cannot be used with an external EV charging point. Would it be acceptable to disconnect the 6mm PME earth from the gas pipe and connect the 10mm cable to the EVSE earth rod?
No
 
My house has a PME earth system. The gas pipe in the garage has a 6mm earth wire already but I've been told this should be changed to 10mm.I'm having an EV charging point fitted externally which required an earth rod to be installed (32ohms impedance measured)-PME cannot be used with an external EV charging point. Would it be acceptable to disconnect the 6mm PME earth from the gas pipe and connect the 10mm cable to the EVSE earth rod?
No. It'll be a bonding conductor (not an earth wire), which needs to be connected to the main earthing terminal near the incoming electrical supply, not a separate rod.
 
I would say no on the basis the existing 6mm is running to the house CU / MET and the advice you have is that this needs to be upgraded to 10mm - back to the CU / MET.
 
Make the entire garage TT bond the gas in the garage to the TT system. The EVC point can then be connected to the TT system. Run a seperate 10mm bond from TNCS MET In the house to point of entry of the gas to the house. Assuming garage has own board and RCD.

Edit: ignore this as I assumed it was detached from the house.
 
Last edited:
Hi Phil - let me paraphrase a sentance from the EV charging Code of Practice section 6.6 "when an EV charging point is supplied from a dwelling with PME, earthing and bonding require careful consideration". Then there's the EV section 722 in BS7671, another riveting read, no doubt.

It sounds like your gas bonding was not up to scratch from a change to PME and so that just needs to happen. The design of the EV system is another thing, imho :)
 
Last edited:
upload_2017-8-11_17-51-0.png
we will have to wait on this one!
 
Oh, that's why you are 'top poster of the month' - still beats the drivel that westy used to come out with though!
 
Sorry westy. Just trying to make Tel feel better about being 'top poster of the month' not everyone can handle the responsibility whereas YOU, now you excel at being TPOTM.
Would you like to enlighten me with examples of this drivel.
 

Reply to Earthing a gas pipe in attached garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock