Hi, just new here..

Just a quick question... as you have your live and neutral and earth, but both your neautral and earth are joined at your incoming and neutral is earthed at your transformer side.

Your neutral being your return feed, why does it have no voltage coming back or little, even tho it's a return? When you short out live to neutral? Why does it trip the mcb even though it's a return
 
Hi Paul - the neutral and the installation earth are not always joined at the service head. TNCS is, TT and TNS are not. As you say the suppliers transformer has neutral connected to Earth. And this is the reason the neutral at the installation has very little voltage on it, relative to the general mass of the Earth. Hopefully.
 
The Neutral does have voltage coming back, you are just not able to measure it using standard methods.
To measure the voltage, you would need to break the Neutral and insert a volt meter between the break.
Measuring between neutral and Earth would be the same as measuring between neutral and neutral.
Shorting out the Line and Neutral causes the MCB to operate because there is nothing in circuit to limit the current.
 
Only in a TNCS are the earth and neutral connected in the DNO cut out and then form the combined pen conductor back to the transformer.
A TNS has a separate earthing conductor all the way back to the source
 
Ah okay thanks guys. So when you short out the neutral live or live to earth the mcb will operate as it gets a surge of current, which trips the mcb?
 
Ah okay thanks guys. So when you short out the neutral live or live to earth the mcb will operate as it gets a surge of current, which trips the mcb?
basically yes. the highewr the current L to N, the faster the MCB will trip. if you have a copy of the regs, the time/current graphs are in appx. 3.
 
If you had a ze on a TNCS of 0.10 ohms then the live to neutral loop will be the same if not very similar.
This gives a fault current at the origin of 2300amps or 2.3ka.
By the time you get to a circuit then the resistance will have increased and you may get say 400 amps of fault current live to neutral or live to earth at say a fault on a socket outlet circuit.
This amount of current will trip the mcb rather quickly.
The tables in appendix 3 only give the fault/time characteristics of a time of between 0.1-5 seconds.
Example would be a 32 amp type b mcb will need 160 amps to instantaneous trip at 0.1-5 seconds.
 
Hi, just new here..

Just a quick question... as you have your live and neutral and earth, but both your neautral and earth are joined at your incoming and neutral is earthed at your transformer side.

Your neutral being your return feed, why does it have no voltage coming back or little, even tho it's a return? When you short out live to neutral? Why does it trip the mcb even though it's a return
Think the OP needs to understand Voltage doesn't flow, come back etc, the live and Neutral are at different potentialshttps://www.youtube.com/watch?v=1xPjES-sHwg
 
The Neutral does have voltage coming back, you are just not able to measure it using standard methods.
To measure the voltage, you would need to break the Neutral and insert a volt meter between the break.
Measuring between neutral and Earth would be the same as measuring between neutral and neutral.
Shorting out the Line and Neutral causes the MCB to operate because there is nothing in circuit to limit the current.

probably a simple answer but if this is the case, why during the safe isolation process would you measure N-E?
 
ok but my point is, lets say your measuring N-E at a CU, technically your measuring N-N are you not?

If the CU is at the origin of a TNCS installation then yes you pretty much are, assuming the tails are the right way round in the cutout.

The thing with safe isolation is that you test everything as its not worth risking your life on assumptions
 
Absolutely. It just dawned on me that essential at a cu point on tncs N-E is essentially N-N. but like you say, always check everything
Think about when your doing an IR test as well.
If you don't isolate the neutral at the main switch you essentially will get 0.00 Mohms with a neutral to earth insulation resistance test
 

Reply to Earthing and neutral help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
598
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated...
Replies
17
Views
2K
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
976

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock