Hi all,

I'm in need of a bit of clarity on this decision.

So, long story short... have been asked to quote for the installation of some electrical services. Property is a small holding, my bad, but didn't check existing earth as there was a lot of items discussed (given it's location, I suspect it's TT as it's an overhead supply), but key ones are provision of various bits outside in a barn and a shed. Barn is attached to property, shed is not. So, I'm planning a small plastic CU inside a weatherproof steel cab inside the barn, fixed wiring will be SWA to try and reduce rodent problems.

My plan is to provide an earth in the vacinity of the barn by way of a rod or structural steel that penetrates the ground (if there is any, not sure there is). If the structural steel doesn't penetrate the ground, I'll be bonding it anyway. Thus creating a TT installation for the outdoor power.

Supply to barn is from main CU by way of a 30mA RCD protected circuit, so I don't need to worry about localised RCDs. I know it would be preferable to have the RCDs local to the board, but the cable is already in place, it's T+E and runs through the building so I'm inclined to leave the RCD at the source.

Am I on the money or way off? If you guys need more info, please let me know and I'll be happy to provide :)

Thanks
 
Hi,just a quick glance,and i am afraid the SWA is not rodent proof,if they are an issue,they will open the armouring to corrosion everywhere they nibble. Maybe consider some containment of a galvanised variety? :)
 
Hi,just a quick glance,and i am afraid the SWA is not rodent proof,if they are an issue,they will open the armouring to corrosion everywhere they nibble. Maybe consider some containment of a galvanised variety? :)

I have considered conduit, I think the price may put them off. To be honest, she mentioned a rodent problem (and there was some evidence a cable being damaged near ground level), but around the barn, the cables already there (not connected) are T+E and I saw no other evidence of meeces, so I'm fairly happy with the choice of SWA. I wouldn't be using the armour for earthing (I prefer not to) just for the additional mechanical protection.
 
You may find that even with overhead supply there's a pme. A lot round here have.

Yeah, I'm seeing overheads converted to PME here too, but 705.411.4 states TN-C system shall not be used (705 is relevant because there are animals present), so unless I'm misunderstanding this regulation I'm required to use TT earthing for this work.
 
What will the barn be used for? Any possible livestock involved?

There is a yard with chickens, two pygmy goats, some guinea fowl, a couple of donkeys in the field next door, so I think yes :)

It was the old milking barn, still got some of the old machinery in there.

This is why I was referring to section 705.
 
Hi
I wasn't considering the full implications of your design. Just a general observation on overheads and pme. I'm sure there's no misunderstanding on your part.
Have fun.
 
Hi
I wasn't considering the full implications of your design. Just a general observation on overheads and pme. I'm sure there's no misunderstanding on your part.
Have fun.

That's why I'm asking though... I'm not sure whether my interpretation (and thus my proposed solution) is correct.

In the space of a week, I've got two jobs come up, one on a working farm and the other on this small holding, where I've got the issue of earthing to seriously consider so I'm just wanting to double check my thinking.
 
I've just done a similar job, installed a rod and bonded the structural steel.

Spoke to the bloke in charge of installing the cut out who made it very clear that I was not to use the PME terminal. Then a man came to install the meter and refused to do it because there was no earth in the PME terminal!
 
Yeah, I'm seeing overheads converted to PME here too, but 705.411.4 states TN-C system shall not be used (705 is relevant because there are animals present), so unless I'm misunderstanding this regulation I'm required to use TT earthing for this work.
You can use TT, TN-S or TN-C-S but certain requirements are needed should the latter be employed and some suppliers may not provide TN-C-S for agricultural sites. TN-C is the only system not to be used and I have yet to come across this in the UK.
 
You can use TT, TN-S or TN-C-S but certain requirements are needed should the latter be employed and some suppliers may not provide TN-C-S for agricultural sites. TN-C is the only system not to be used and I have yet to come across this in the UK.

Then I was misunderstanding that as I was assuming it was a short form for TN-C-S... and I must admit I did ponder what other TN-C-? it could have been other than TN-C-S, so I've learned something today :)

But on a serious note, have been doing a bit more reading about this I don't have a suitably sized earthing conductor that I can connect to the MET at the incoming supply, regardless of earthing system in use, and getting one from one corner of the house to the other will be a problem.

So, I'm going to install a rod (or use the metal structure of the barn if it is in good contact with the earth) and create a TT earthing system for the external electricals, which will include bonding the metal work of the barn.
 
The "certain requirement" for using a TNC-S could be rather expensive.

This is taken from :

Electrical Contractors guide to wiring Regs 17th edition. (Does not include amendments)

If a bonded metal grid cannot be laid in the floor of animal houses during construction or refurbishment, it is recommended that a TN-C-S (PME) electricity supply is not used. A TN-S supply is preferred. If a TN-C-S supply is offered or is the only type available, it is recommended that a separate local earth electrode be installed.

I think your ok with your design but don't take my word for it.
 
I like the TT solution for remote agricultural buildings. The barn is attached to the dwelling and so it should have a metal containment for the CU as you say. But there's a 5 way IP rated metal one from BG that's good value, if it was big enough.
Bg - Search Results | NoLinkingToThis - https://www.NoLinkingToThis/search?search=BG

IMG_0831.JPG
 
Last edited:
TT earthing for the barn sounds like a good plan in this case.
Remember to ensure that all extraneous parts are bonded and consider if supplementary bonding would be useful for reduced touch voltages if there is a lot of metalwork in the barn.
I would read and apply section 705 for this installation, even though it is not too onerous.
Keep cables high and out of reach where possible and consider appropriate protection if they are in reach of animals.
 
I like the TT solution for remote agricultural buildings. The barn is attached to the dwelling and so it should have a metal containment for the CU as you say. But there's a 5 way IP rated metal one from BG that's good value, if it was big enough.
Bg - Search Results | NoLinkingToThis - https://www.NoLinkingToThis/search?search=BG

View attachment 38887

See, I was planning on separating the barn and out house/shed circuits (which means 4 in total). There will be a buried SWA segment linking the two buildings and I thought I'd separate the circuits to allow that segment to be turned off completely in case of a fault whilst maintaining the services in barn. If I combined lighting circuits I could make do with that CU, but then there is no room for expansion.

That's where the cost is coming from as I'm looking at a small customisable plastic CU inside a metal weatherproof cabinet.

I did actually consider two of the BG units... one for the main switch for this section and then the other for the OCPD, but I think that looks a little bad.

If anyone knows of a nice cheap 6 way weather proof CU that is Amd 3 compliant, I'd love to know about it :)
 
If the structural steel doesn't penetrate the ground, I'll be bonding it anyway.
I think I may be being a bit thick here but why would you bond it? So how do the supply to the (three?)other sheds work? Are you daisy chaining it or supply to each from main supply? Sorry if this is all obvious.
 
I think I may be being a bit thick here but why would you bond it? So how do the supply to the (three?)other sheds work? Are you daisy chaining it or supply to each from main supply? Sorry if this is all obvious.

I think what I should have said, is I'll be doing some checks to establish if the metal work is considered extraneous and bond it accordingly. There is metal work in the barn that will need to be evaluated, old equipment and such like.

The supply goes like this:-

SUPPLY -> HOUSE CU -> T+E -> ATTACHED BARN

From the barn, it's a short hop (about 2m) to a detached shed/out house where they want some lighting, power and an outside socket for a pond.

Currently there is a T+E in place and terminated at the CU, it's just not turned on which is a good thing as the other end is just coiled up with a bit of PVC tape over the end from what I could see.

The plan is to put a CU in the barn on the end of the T+E and run SWA to the other places... 1.5mm 3 core for the lighting, 2.5mm 3 core for the power with a 2.5mm 4 core for the hop to the shed/out house so I'm only running one cable.
 
Last edited:
So if the Barn or outhouse develop an earth fault and you are relying on the CU RCD in the house then all the house goes out with the outside buildings if I am understanding this correctly?
 

Reply to Earthing for an outdoor install in a barn in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
551
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K
Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
950
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hey guys, looking for a bit of advise on the installation of an outside light. I plan on chasing out the plasterboard and running a cable from a...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock