a spark..its a no from me
Thanks anyway Sharon..
Discuss Earthing from over head lines... in the Australia area at ElectriciansForums.net
a spark..its a no from me
Phone DNO and find out if they are supplying an earth, if not fit Earth rods. Not that difficult is it?
Thanks anyway Sharon..
Had this about 3 months ago, overhead lines coming into property - 1 cable, just like pme, looking down the street every 3rd or so pole had earth cable coming down it, looking like pme, there was a 16mm earth at the cut out that went inside to the consumer unit, but not connected at either end, there was and old earth stake which was connected, so i'm thinking here we have an old TT installation, that the overhead wiring has been converted to pme but the house has not been, phoned e-on and got directed and re-directed, listened to lots of pretty music whilst "on hold" and the answer??? "we dont actually know what type of wiring we have in that area" !! jesus christ!!! suffice to say even though there could have been a lovely low pme Ze to be had, i left the installation as a TT because at least that way i could confirm the earth arrangement!!
So can sympathise with OP, cause sometimes things aint what they may seem, could be TT could be overhead pme, but obvious lack of any earth would dictate to rod it and TT it, oh and the DNO??? i dont know why people say to call them, next to useless advice in my experience
Blimey, the arms membership bar has been lowered!
the OP said there was no earth, how can you do a Ze with no incoming earth??
I thought it had been raised, I’m bared!
Do you want to have a think about that for a minute?
a good majority of the supplies up here are from over head lines and they are mainly TNCS ,occaisionally TT ,this may be a silly question but have you done a Ze , I bet the RCD you are talking about is an old brown one if im not mistaken they were outlawed in a change of the regs back in 1984 or around that time as jason has said contact the DNO for advice
I've had a think about it, so how Do you get an earth Ze value at the cut-out/CU ?? You can get a neutral Ze, but nothing to compare it with, the installation doesn't even have any services bonding in place....
If you test between line & earth, this would give you an indication that PME could be available.
Can't rule out PME without seeing the cutoutThat was the point, there is no earthing available anywhere to test!!
Can't rule out PME without seeing the cutout
That was the point, there is no earthing available anywhere to test!!