Discuss Earthing of a remote sub consumer unit in the Australia area at ElectriciansForums.net

F

flattop

Hi I need to fit a sub consumer panel (I am not sure if that is the correct term) in a seperate outbuilding, from the main consumer unit in the house.
(a)Do I need to run a 3 core with earth, so that it is earthed at the same point as the house? or
(b)can I run a 2 core and use the earth on the outbuilding, which is good?
It is about 20m away.
any advice would be most welcome. Thanks in avance. Jane
 
There are pros and cons to both methods.

If the house is a TN system and you intend to extend the equipotential zone out to the outbuilding, then yes maybe worth considering running a 3 core out if you have water/gas services. Using a 3 core 10mm, you could use the 3rd core as a bonding conductor and the SWA as your CPC.

If you have already a TT earth for the house, then I would most certainly run a 2 core and rod the outhouse and tie the earthing rods together via the SWA CPC.
 
cpc -- circuit protecfive conductor. SWA -- steel wire armoured (cable). i would however question your ability to complete this job, going from your posts. it is notifiable work ( assuming you are in england (12) or wales (19))
 
Last edited:
Hi I need to fit a sub consumer panel (I am not sure if that is the correct term) in a seperate outbuilding, from the main consumer unit in the house.
(a)Do I need to run a 3 core with earth, so that it is earthed at the same point as the house? or
(b)can I run a 2 core and use the earth on the outbuilding, which is good?
It is about 20m away.
any advice would be most welcome. Thanks in avance. Jane

When you say earth on the outbuilding?Cant understand what you mean exactly??

Sent from my GT-I9100 using Tapatalk
 
Thanks for the information, and don't worry, I am not going to do the work. I just wanted to check the best approach before commissioning it. Cheers, Jane.
 
Nothing to stop you connecting this earth electrode, to any earth system your bringing to this outbuilding. If the house earthing system is PME/TNC-S, then you would need to run a 3rd core 10mm if there is any water service incorporated in this outbuilding. But you can still incorporate this existing earth electrode into your system.....

As others have mentioned you don't seem to be too sure of what your doing, so i strongly recommend you employ a qualified electrician. You can always come to some arrangement such as you providing the cable trench etc, which will reduce the cost of employing a qualified electrician. Remember, it can be substantially cheaper to employ a Part Pee electrician than to do this work yourself and notify yourself!! Just to notify the LABC could set you back 250 quid!!!
 

Reply to Earthing of a remote sub consumer unit in the Australia area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
693
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
20
Views
4K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
264
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock