    Hi I need to fit a sub consumer panel (I am not sure if that is the correct term) in a seperate outbuilding, from the main consumer unit in the house.
    (a)Do I need to run a 3 core with earth, so that it is earthed at the same point as the house? or
    (b)can I run a 2 core and use the earth on the outbuilding, which is good?
    It is about 20m away.
    any advice would be most welcome. Thanks in avance. Jane
     
  2. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    There are pros and cons to both methods.

    If the house is a TN system and you intend to extend the equipotential zone out to the outbuilding, then yes maybe worth considering running a 3 core out if you have water/gas services. Using a 3 core 10mm, you could use the 3rd core as a bonding conductor and the SWA as your CPC.

    If you have already a TT earth for the house, then I would most certainly run a 2 core and rod the outhouse and tie the earthing rods together via the SWA CPC.
     
  3. flattop
    Offline

    flattop Guest

    thank you very much I think I understand except what is a cpc and SWA? Sorry to be so ignorant! Jane
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    cpc -- circuit protecfive conductor. SWA -- steel wire armoured (cable). i would however question your ability to complete this job, going from your posts. it is notifiable work ( assuming you are in england (12) or wales (19))
     
    Last edited: Feb 25, 2012
  5. SimpleSimon
    Offline

    SimpleSimon Guest

    Location:
    Yateley
    When you say earth on the outbuilding?Cant understand what you mean exactly??

    Sent from my GT-I9100 using Tapatalk
     
  6. flattop
    Offline

    flattop Guest

    Thanks for the information, and don't worry, I am not going to do the work. I just wanted to check the best approach before commissioning it. Cheers, Jane.
     
  7. flattop
    Offline

    flattop Guest

    Its a large post driven into the ground to attach earthing wires to. Reading 42ohms.
     
  8. Engineer54
    Offline

    Engineer54 Guest

    Nothing to stop you connecting this earth electrode, to any earth system your bringing to this outbuilding. If the house earthing system is PME/TNC-S, then you would need to run a 3rd core 10mm if there is any water service incorporated in this outbuilding. But you can still incorporate this existing earth electrode into your system.....

    As others have mentioned you don't seem to be too sure of what your doing, so i strongly recommend you employ a qualified electrician. You can always come to some arrangement such as you providing the cable trench etc, which will reduce the cost of employing a qualified electrician. Remember, it can be substantially cheaper to employ a Part Pee electrician than to do this work yourself and notify yourself!! Just to notify the LABC could set you back 250 quid!!!
     
  9. Mr Mike
    Offline

    Mr Mike Regular EF Member

    Location:
    West Midlands
    Very good tel
     
Loading...
Similar Threads - Earthing remote consumer Forum Date
Spiritual Earthing.. Electrical Forum Saturday at 6:31 AM
Earthing arrangements to a generator and change over switch Electrical Forum Thursday at 6:21 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job