Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Earthing question?

Discussion in 'Electrical Forum' started by Ross1, Feb 22, 2012.

Discuss Earthing question? in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Ross1
    Offline

    Ross1 Electrician's Arms

    Hi guys, I've got 2 x 10mm/sq at cu. 1 of them is giving me a ze reading of 176 ohms and the other 1 won't test on my fluke mf 1653b it is a tt install but no sign of rod.

    How do I tell wether I'm getting a reading thru the gas or water bond, no signs of bonding any where.

    Thanks
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    first if there's no bonding to gas or water, tou won't get your Zeaffected by them. yhis needs further investigation, as in find the rod or fit a new one , then go from there. get the bonding installed etc.
     
  3. WPD Lad
    Online

    WPD Lad Guest

    What's in the MET?
     
  4. 1shortcircuit
    Online

    1shortcircuit Guest

    Are you sure there is an earth?

    Is the system definitely TT and not an alternative supply missing an earth connection?

    Always useful in situations like this if you take a picture to upload, even phones will do in most cases:thumbsup

    *** Edit - Just read the comment about no sign of any bonding anywhere *** ;)
     
    Last edited by a moderator: Feb 22, 2012
  5. Ross1
    Offline

    Ross1 Electrician's Arms

    There is no MET, just 2 10mm/sq single earths disappearing into wall.

    Why am I getting 100 odd ohms on the one 10mm and then when testing on the other 10mm my tester makes a funny noise and won't test......think it comes up with error code 4. Im testing both exactly the same.
     
  6. 1shortcircuit
    Online

    1shortcircuit Guest

    Are you getting sound contact on all terminals? I had a similar situation the other day when testing for Zs on a shower and I was adamant that I had sound contact but I had a re-shuffle, unplugged leads and re-plugged gave the fused connectors a good push to ensure they were connected properly and I then obtained a satisfactory reading.
     
  7. Ross1
    Offline

    Ross1 Electrician's Arms

    Yeah checked all contacts etc
    keeping in mind that this is a house that been renovated about a year ago (full rewire) no ring mains, spurs from many sockets, 2 socKets never worked. DIYer by the looks. Old board with no cover on it, so any thing possible here if you get my drift
     
  8. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    is this a semi?....or a terrace?.....shared supply maybe....just because you have a cutout at the C/U for this house doesn`t mean owt.......could be that the supply comes from next doors cutout into yours and its THEIR earthing arrangements or extranious that your reading.....
     
Loading...
Similar Threads - Earthing question Forum Date
Earthing arrangements to a generator and change over switch Electrical Forum Yesterday at 6:21 PM
High Zs on SWA Armour / New Earthing Conductor Periodic Inspection Reporting & Certification Yesterday at 2:22 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job