Discuss Earthing System Advice in the Commercial Electrical Advice area at ElectriciansForums.net

sajeel

-
Reaction score
49
Hi
Saw a mates job the other day where the supply is three phase, however there was two earthing system at head there was tn c s and tn s. So there was separate earth clamped on supply wire to main earth terminal and a additional earth wire run which was connected to neutral of supply ?
Didn't think this is normal practice although dno have recently been to replace fuse ?
Then consumer was wired one earth in earth terminal and the other earth in neutral ?
 
thanks for replies, both the posts make sense, so if tn-c-s was upgraded then there would be two earth wires in terminal of cu ? or both fed to a met and then one wire fed to cu ?
 
Hi
Saw a mates job the other day where the supply is three phase, however there was two earthing system at head there was tn c s and tn s. So there was separate earth clamped on supply wire to main earth terminal and a additional earth wire run which was connected to neutral of supply ?
Didn't think this is normal practice although dno have recently been to replace fuse ?
Then consumer was wired one earth in earth terminal and the other earth in neutral ?
Possibly hi Z so belt and braces!!!
 
I would have expected a DNO notice,at the head,to give some details....not always done,but that is taking it,that the supplier did the mod ;)
 

Reply to Earthing System Advice in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
522
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
438
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock