Discuss Earthing Via the SWA on sub mains??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
15
Hi Guys, I have a question for you and no doubt I will have more as the week progresses:dizzy2:. I started a new job and I'm doing a 5 year periodic on a residential care home I have previous experience on domestic installations but this is by far the biggest thing I've taken on.
My question is this, the intake room has a three phase supply which feeds DB1, this in turn feeds 7 other 3 phase distribution boards via SWA sub mains cables. The problem I have is that none of the sub mains have a cpc conductor and are earth via the SWA itself, some of the brd's have 10mm earths connecting the earth bar to the sub main banjo and some are only connected via the gland and case itself. On all but two of the brds I have good EFLI readings and the other two are high 0.27?
Is this type of arrangement acceptable or do they need to have new earth installed back to the main dist brd.
 
the Gland needs to have a fly lead back to the Earth Bar on all joints if this arrangement is used to supply a Earth

other than that 0.27 as a ZdB thats fine...!!

what earth is in the property TN-S or PME
 
the Gland needs to have a fly lead back to the Earth Bar on all joints if this arrangement is used to supply a Earth

other than that 0.27 as a ZdB thats fine...!!

what earth is in the property TN-S or PME
PME

So all what code would I put on the SWA with no connection to the earth bar within the dist brd. C1???
 
the fact that the SWA lock nut is glanded to a steel box does not make it immediately dangerous as you have obtained a relevantly good ZdB reading of 0.27. rules out code 1

but on the flip side its against the regs past and present so it cant be code 3

personally i would give it Code 2 (still a fail) as it could potentially be a problem in future if some one snapped the gland out the Db or some thing...!
 
If the equipment is made from a conducting material, and that equipment is realiably and effectivley connected to earth, then a fly lead is not required. The gland must be in good contact with the equipment though. The same principles apply to MICC, SWA, steel trunking and conduit.
 
If the equipment is made from a conducting material, and that equipment is realiably and effectivley connected to earth, then a fly lead is not required. The gland must be in good contact with the equipment though. The same principles apply to MICC, SWA, steel trunking and conduit.

Agree, .... A good method would be using a biting type nut as the locknut, such as a ''Piranha nut''!!... lol!!
 
Agree with johnboy and engineer54, there is no 'absolute requirement' for a banjo and flylead. In many cases a serrated washer is better. As long as the paint is scratched off beneath the gland and it is done up properly, and I got good readings, I would not code it. I would definately check that the armouring is of a suitable size to be used as a cpc though.
 
Agree with johnboy and engineer54, there is no 'absolute requirement' for a banjo and flylead. In many cases a serrated washer is better. As long as the paint is scratched off beneath the gland and it is done up properly, and I got good readings, I would not code it. I would definately check that the armouring is of a suitable size to be used as a cpc though.

Very slim chance that the SWA armuoring wouldn't comply, if the conductor core sizes are under 95mm, even for 2 core!! If very long runs, then i would maybe start doing a few calculations, just to satisfy myself...
 

Reply to Earthing Via the SWA on sub mains??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
438
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
723
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock