My question wasnt about the correct way to install etc im aware of all points people have mentioned... More on how far would people go ensuring everything inline was adequate simply to provide just a quote and what tests would you carry out as could be very time consuming in this circumstance. Also on what details you would input on EIC as some have said they would only check submain woring on and mains. As we know alot would install without a thought. Explainig to clients isnt simple either, especially if it creates more work as "its been like that for years"will be their reaction...but taking into account all the points being made on adequacy of current installation etc would you just refuse to do anything unless all points are met. Thanks for replies peeps. In terms of discrimination it is as follows. I shouldve been more clear with details at start apologies...
Cutout
3phase 100A bs1361 feeds
DBmain (8 way)
3P MCB 60Amp 16mm4c (swa cpc) feeds
DB1 - 3Phase (8 way)
3P MCB 63A dont know cable size feeds
DB2 which has a 100A RCCB 30mA main switch and is 3 phase.
32 A single phase mcb (attached image) 6mm 3 c swa feeds
DB 3 which has 100A RCCB 30mA main switch single phase 5 way DB.. Think thats pretty accurate but is from memory as details are in the van which is outside and its cold .
 
My question wasnt about the correct way to install etc im aware of all points people have mentioned... More on how far would people go ensuring everything inline was adequate simply to provide just a quote and what tests would you carry out as could be very time consuming in this circumstance. Also on what details you would input on EIC as some have said they would only check submain woring on and mains. As we know alot would install without a thought. Explainig to clients isnt simple either, especially if it creates more work as "its been like that for years"will be their reaction...but taking into account all the points being made on adequacy of current installation etc would you just refuse to do anything unless all points are met. Thanks for replies peeps. In terms of discrimination it is as follows. I shouldve been more clear with details at start apologies...
Cutout
3phase 100A bs1361 feeds
DBmain (8 way)
3P MCB 60Amp 16mm4c (swa cpc) feeds
DB1 - 3Phase (8 way)
3P MCB 63A dont know cable size feeds
DB2 which has a 100A RCCB 30mA main switch and is 3 phase.
32 A single phase mcb (attached image) 6mm 3 c swa feeds
DB 3 which has 100A RCCB 30mA main switch single phase 5 way DB.. Think thats pretty accurate but is from memory as details are in the van which is outside and its cold .
That is very poor discrimination between RCD's if something with a earth fault is plugged in on DB3 this could trip out DB2.
 
So the situation changes again.
You have no discrimination between boards and you now have no discrimination between RCDs as well.
So a short circuit at DB3 could readily take out DB 2 as well.
An earth fault DB3 will also take out DB2.
However this is not what you are installing. Though you would need to check the RCD is working which will be a nightmare of overlap.
Since you are doing a rewire of a whole area, I would say that you should also attempt to find out the supply cable size between DB1 and DB2.
Then you will be able to enter the circuit description details of the submains on the EIC, Zdb only being relevant at DB3.
Full circuit details and tests would be needed for the circuits you are rewiring from DB3.
Part rewire boards.gif
 
That is very poor discrimination between RCD's if something with a earth fault is plugged in on DB3 this could trip out DB2.
Client says it occasionally trips at DB2 but it only feeds a couple of sockets and a light within the outbuilding the db is located in( which isnt occupied) and a greenhouse db so isnt a major inconvenience..
 
So the situation changes again.
You have no discrimination between boards and you now have no discrimination between RCDs as well.
So a short circuit at DB3 could readily take out DB 2 as well.
An earth fault DB3 will also take out DB2.
However this is not what you are installing. Though you would need to check the RCD is working which will be a nightmare of overlap.
Since you are doing a rewire of a whole area, I would say that you should also attempt to find out the supply cable size between DB1 and DB2.
Then you will be able to enter the circuit description details of the submains on the EIC, Zdb only being relevant at DB3.
Full circuit details and tests would be needed for the circuits you are rewiring from DB3.
View attachment 41417
Also the 63A @ db1 after the 60@ dbmain
 
Into DBmain from metering. Poor installation all round really. Main earth looks to be 10mm to met then 25mm into dbmain. Cant see incomer as 2 obsolete cables are cut sticking out covering it.

Screenshot_2018-03-17-20-28-56.png

Screenshot_2018-03-17-20-28-48.png
 
That looks a lot like one of the tails entering through a separate hole in the steel enclosure, so you’ve got another non-compliance.
That's it Dave kick him when he's down, these non-compliances are acuminating.And there is abrasive edge (no bush/Gromit to cable entry on left.
 
Observed, thats why i took the pic. Its Neutral and Earth. Also no lid for the trunking header which creates an Ip4x issue in top of db. I think these old brown tails are single insulated? Again where would you go with these. Observations on existing installation could be alot of work alone. These would hopefully have all been highlighted in the latest eicr.
 
Last edited:
Non compliance’s which do not result in danger or potential danger can be left and a comment made on the EIC.
It would be down to the installer to decide what constitutes a danger to the existing installation such as any possible eddy current issues which have been identified.
Look for any thermal damage to the surrounding enclosure etc.
If it can be rectified then do so.
 

Reply to EIC for submain db rewire in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
1K
Apologies for the complexity of this question, but there’s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock