O
ohmslow86
Hi,
scenario is. TNC-S 100A BS1361 main fuse at DNO cutout. 16mm tails feeding meter. 2x 16mm T&E cables coming out of meter (no switch fuse) going through wall (un-protected) up cavity across attic to the House DB and storage heating DB-both 15m away. Ze-0.17 pfc-1.32
The 6mm CPCs from the T&E are connected to the cutouts MET. A single 6mm Earth going away from MET to bond water supply. All extraneous parts inside bonded in 6mm.
House DB made up of 2x 2kw convectors, 8.5kw shower, 5.5kw free standing cooker, 2x32A ring mains,1x Immersion heater. Storage HTG DB has 1x2.8 kW. All RCD protected.
Is the 16mm TE undersized to take load of House DB?
Table 4D5 suggests CCC using method 101 is 57A for 16mm TE. So, am I correct in giving this a Code 2? Even though this is original wiring when house was built (1 up 1 down) and there are no signs of thermal damage at either ends...
Is the DNO 100A main fuse sufficient protection for the 16mm TE?
I need to get my wording spot on as the Landlord is a retired spark!
Input please. Thanks
scenario is. TNC-S 100A BS1361 main fuse at DNO cutout. 16mm tails feeding meter. 2x 16mm T&E cables coming out of meter (no switch fuse) going through wall (un-protected) up cavity across attic to the House DB and storage heating DB-both 15m away. Ze-0.17 pfc-1.32
The 6mm CPCs from the T&E are connected to the cutouts MET. A single 6mm Earth going away from MET to bond water supply. All extraneous parts inside bonded in 6mm.
House DB made up of 2x 2kw convectors, 8.5kw shower, 5.5kw free standing cooker, 2x32A ring mains,1x Immersion heater. Storage HTG DB has 1x2.8 kW. All RCD protected.
Is the 16mm TE undersized to take load of House DB?
Table 4D5 suggests CCC using method 101 is 57A for 16mm TE. So, am I correct in giving this a Code 2? Even though this is original wiring when house was built (1 up 1 down) and there are no signs of thermal damage at either ends...
Is the DNO 100A main fuse sufficient protection for the 16mm TE?
I need to get my wording spot on as the Landlord is a retired spark!
Input please. Thanks