B

bobby101

hi all i would like some advice if possible, i came across a situation that is annoying me, a small retail outlet a tp&n db fed of 15mtr run of swa which is controlled via a seperate isolator at cable head

1: the db didnt have a, frying pan or a seperate earth from swa to the met, which i would consider to be the main earth bond, should i just highlight this and just state db fed from swa if this is the case how should i rate the catagory in the eicr

2: the main isolator at cable head had trunking between cable head and isolator, the trunkning was missing the lid and main tails were bent in such a way that no lid woud possibly fit the trunking, which was undersized but the area was behind a cuboard door comments please
 
hi all i would like some advice if possible, i came across a situation that is annoying me, a small retail outlet a tp&n db fed of 15mtr run of swa which is controlled via a seperate isolator at cable head

1: the db didnt have a, frying pan or a seperate earth from swa to the met, which i would consider to be the main earth bond, should i just highlight this and just state db fed from swa if this is the case how should i rate the catagory in the eicr I assumed you meant the banjo tag, but we all call it different things I guess. As the SWA is classed as an exposed conductive part and if it is not earthed then reg 411.4.2 is not being adhered to and so I would code that a 2. Is there a CPC in the SWA, ie a 3rd core? Have you checked for continuity, if the trunking is metal and the DB metal also it might be giving you an earth path, if it is then really you can't code it anything.

2: the main isolator at cable head had trunking between cable head and isolator, the trunkning was missing the lid and main tails were bent in such a way that no lid woud possibly fit the trunking, which was undersized but the area was behind a cuboard door comments pleaseIf the main tails are single insulation ie not the double sheathed then by not being able to fit the lid then they are contravening reg 521.10.1 and again for that I would code it a 2. This is before we even start to use good workmanship etc etc

............................
 
Last edited:

Reply to eicr and test help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Hello everyone i recently got a job on replacing a BMS panel in a plant room. the NEW panel i installed except the control side of the...
Replies
8
Views
1K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 >...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock