Discuss EICR audits _________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

The company I work for periodically gets its EICR'S audited, one thing they pulled us for was plastic blanks in pre Amd3 boards 'easily removed without the use of a tool and readily accessible'
They put this down as a 'code 2'
Can't really fathom this, what about pendants? Which have been overlooked, it's resulted in a return to hundreds of properties fitting MCB blanks.
Any thoughts?
Don't you mean the company that you work for has an EICR done periodically if that's how I read it? what hight is this distribution board? if you can stand there and push the blank in then you have direct contact with live parts so fixed blanks would be required they are not expensive.
 
Just because they can be turned off internally doesn't mean mean that they are turned off. So it must follow that does not give you exception to install blanks that are removable without a tool.
Merlin gerin blanks fit tight in the boards and come in strips of five I would say that these blanks would not be able to be removed without a tool . The only full dinrail blanks I know of are the mem memshield 2 and hager , do any other manufactures make them ?
 
So there is still lot that only make clip in blanks . What about wylex , crabtree, schnider, BG, chint, etc . May be glueing them in is the answer, just not very handy for the next man who comes along to install an extra circuit:mad::)
 
re lampholders, if they were designing them today they'd probably not have exposed contacts (or in reality, the trend for non replaceable LED lamps will continue until they are eventually mandated)

and I think the concern about "not accessible without a tool" is more about kids pulling them out than preventing your average DIYer. Enough people are scared to touch a CU in the first place, even those who are are less likely to go at them with a screwdriver!

all regs are open to interpretation and professional judgement, to the letter the inspector is spot on, but perhaps judgement would be used depending on the location of the CU and use of the bulding.
 
Crabtree brought out a safety pendant holder a fair few years back where the pins were not live with the lamp removed, never really caught on.
 
The company I work for periodically gets its EICR'S audited, one thing they pulled us for was plastic blanks in pre Amd3 boards 'easily removed without the use of a tool and readily accessible'
They put this down as a 'code 2'
Any thoughts?
Ok ...we have all probably seen some DBs CSUs with holes, no blanks, some out of reach...if they are falling out then fair comment if they fit well then code 3...quick fix... just spot some super glue on the plastic blanks, they can be cut out later if required. As for amd3 there is nothing wrong with using plastic blanks next to plastic MCBs under a metal lid.
 

Reply to EICR audits _________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had the first EICR done on my flat last week, which failed with some C2s for having an older (2001) plastic consumer unit with no RCDs, but...
Replies
22
Views
3K
The purpose of this thread is two-fold: to let you folks see an EICR from someone who's too lazy (or busy) to even bother forging his test...
Replies
15
Views
3K
Hi all Eicr being undertaken, what code if any would you consider for this scinario Small bathroom in a flat, with airing cupboard inside, no...
Replies
9
Views
2K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock