ChrisElectrical88

-
Mentor
Esteemed
Arms
Reaction score
1,650
Im currently in the middle of a Condition report and i have a defect i cant decide which code to use.
The defect reads as follows:

DB2/4R Water heater girls WC, 2.5mm 32A radial circuit requires downgrading to a 20A radial.

C2 cause it could overheat or C3 as its never going to draw 32A down it?

Im thinking C3?
 
Is it likely that a larger water heater could be put on the circuit if the old one was removed ?
Could the current drawn from the present heater cause the cable to run hot ?
Does the installation method contribute to this ?
Could this cause damage to the cable ?
Could a breaking down element in the heater draw more current than the cable is rated for ?

My action would probably be to C2 it. After all it's a simple remedy to get rid of the coding.
 
Its a 2.2kW water heater so no risk of it drawing anything near 32A, Installation method is clipped direct through the fabric of the building (flat roof so assuming joists and insulation)

Edit: The thought that a larger water heater could be installed is a very good point. I have gone with a C2.
 
Last edited:

Reply to EICR Code in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m interested to hear other views on BS3871 MCBs being changed following a C2 non compliance on an EICR for over rated protective device. Eg...
Replies
9
Views
418
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock