Im currently in the middle of a Condition report and i have a defect i cant decide which code to use.
The defect reads as follows:
DB2/4R Water heater girls WC, 2.5mm 32A radial circuit requires downgrading to a 20A radial.
C2 cause it could overheat or C3 as its never going to draw 32A down it?
Im thinking C3?