had to do an EICR today for a job on which the installer hadn't certified.

Everything was okay but I didn't know what code to give for the following;

the immersion was supplied via off peak supply on its own circuit but the top element was supplied via the ring main? I remember reading in the regs that it has to have its own dedicated circuit. So what code do I give it? I'm assuming a 3 as it's obviously not dangerous but an improvement recommended.

any advice appreciated

thanks!
 
how is the immersion connected to the ring ?
via a fused spur ? then no code.

direct connection without local fusing ? then C2.
 
go to electricians school, get qualified
double pole switch is needed as means of isolation. Fuse / breaker is needed to prevent FIRE. If on ring this 15A element and its cable are probably at 32A. Alternatively put 16 or 20A breaker on ring, now safe but probably will trip when they put the electric heater/toaster on at same time as immersion.
 
and bear in mind that, as a fixed load, overcurrent protection may be omitted. the 32A is more than adequate for short-circuit protection.
 
Appendix H of OSG states any water storage vessel in excess of 15 litres should be supplied by their own separate circuit, also immersion heaters should be supplied through a switched cord outlet connection unit complying with BS1363-4
 
Hi Guys

had to do an EICR today for a job on which the installer hadn't certified.

Everything was okay but I didn't know what code to give for the following;

the immersion was supplied via off peak supply on its own circuit but the top element was supplied via the ring main? I remember reading in the regs that it has to have its own dedicated circuit. So what code do I give it? I'm assuming a 3 as it's obviously not dangerous but an improvement recommended.

any advice appreciated

thanks!

So a new install not done by a sparky?

C2, best on its own circuit............ are you sure its on the ring?
 
"the element is 15A" are they not 3kw anymore ? IE 13amps

And most switch spurs are DP nowadays I am sure ?

Most immersion heaters are 3kw, yes, but some are more...

Most immersion heaters are adequate on a 13a fuse spur - but i agree, a 20a DP switch is better - especially in this case, if the immersion heater is 3.5kw.

Whats the wattage OP ?
 
Yes the element is 3.5kW. I know that a couple of blokes on here are saying I should go to 'electrician school', it's not that I don't know what I'm doing, I'm going it alone after my apprenticeship and just using it to pick other sparks brains on a solution. I thought that was the whole idea of the forum?


So to conclude most agree it's okay on a 20A dp switch staying on the ring main, but ideally on its own circuit?
 

Reply to EICR code in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
798
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
607
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock