Just carried out an EICR on a standard semi which has had some work done in 2015-16. The works included connecting an outbuilding to the rear of the house to create a hall, WC and utility room. The Kitchen was also replaced, new cooker and shower circuits installed.
The 1 sockets circuit does have RCBO protection but is the only one!
Putting the other issues I found to one side, I wanted to know what others thought about this -
As I know the installation date was at a time the regs called for RCD protection everywhere, am I right to think this warrants a C2 for i.e. no rcd for cables >50mm on GF lighting circuit, just for a start..
If installed to 16th I would C3.
Naturally, client has no certs...
But - "he was very good and qualified.."
The 1 sockets circuit does have RCBO protection but is the only one!
Putting the other issues I found to one side, I wanted to know what others thought about this -
As I know the installation date was at a time the regs called for RCD protection everywhere, am I right to think this warrants a C2 for i.e. no rcd for cables >50mm on GF lighting circuit, just for a start..
If installed to 16th I would C3.
Naturally, client has no certs...
But - "he was very good and qualified.."