Ok, so here I am testing/inspecting some new floodlights installed at a local community facility. The installers, in their wisdom scarpered without leaving anything resembling a certificate so I'm doing a EICR on the 2 circuits in question.

The "post" end of the circuits is shown here, there is no lock on the door so anyone with a pair of pliers can gain access:

Post Open.jpg

Inside the connections to the floodlightsare clearly "exposed", the floodlights in question are approximately 20 foot above:

Post Inside.jpg


Now I'm thinking that this should be a C2 as the MCB etc at the very least should be within its own enclosure.

Your thoughts???
 
As you still need a tool of some description to remove the cover suppose C2 would cover it. If door had no fastening mechanism at all then C1.

But I don't do much in the way or EICRs so others will probably stand me corrected
 
I would defo say the mcb needs an enclosure. The ones Ive seen in lamp posts are in a plastic box with a clear front so you can see the mcb. Are the locks on the door them triangle ones like on the white metre cupboards on the side of a house?

Jay
 
I would defo say the mcb needs an enclosure. The ones Ive seen in lamp posts are in a plastic box with a clear front so you can see the mcb. Are the locks on the door them triangle ones like on the white metre cupboards on the side of a house?

Jay

The "locks" aren't triangular like meter cupboards, they are square and not lockable!
 
Not lockable CODE C1 EXPOSED live parts OR tap n screw door shut with a bolt
The "cutouts are best fitted preferably with fuse rather than MCB due to condensation in the pole dripping down
 
Thanks guys, reassuring input.

When I see installs like this I do wonder what was going through the minds of those doing the work when they install like this!!
 

Reply to EICR Coding Opinions please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
488
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
HI , potential 2 bed 1970’s bungalow buyer here…. Our surveyor (RICS) has pointed out there is no circuit breaker to the electrics (fuse board...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock