Welchyboy

I am undertaking an eicr on 20 odd blocks of flats and would like people's opinion on this set up

The blocks are separated be about 30-40 meters apart, each in a typical square shape with stairs in the centre

Have external stairwell areas only, a ground floor and 2 other storys on top, each block has 6 flats, 3 on each side of the stairwells

The supplies/meters for the flats are in flush mounted meter cabinets at the bottom of the stairs
1x TPN 60a PME supply for each side, one phase per flat

I'm only testing the landlords supply!

This is supplied by one meter in a block to a small c.u. Then has 2x 2.5mm SWA sub mains to 2 other blocks each, so one meter supplies 3x landlords blocks, these are in small cupboards on each Block around 600mmx400mm

now I'm happy with most things apart from the fact that each flats water supply comes through this cupboard with the small cu in it

The water incoming is plastic but out going to the flats is copper

If the flats are bonded back to their local supply then the exposed copper
In this small cupboard will bring in a
Different earth potential which is simultaneously accessible to the mini cu earth fed from the PME from the other block


What action would you take if you found this

I know it's long winded, sorry just wanted to give a good picture of the situation
 
Last edited by a moderator:
To get an handle on this WB you have each block with it's own individual water supply which is plastic. Then after the stop cock/valve inside the block the installation to the 6 flats are done in copper?

So I would assume that the first piece of copper pipe after the plastic is the main branch in what 32/40MM and then it 'T's into each flat in what 22mm

So is that main branch (32/40mm) bonded? Is the 'T' once it enters into the flat bonded to the CU in flat? Where do you think this copper installation is getting it's potential from if the incomer is plastic? Is the stairwells Metal? Is the construction pre-cast/concrete?
 
Hey malcomsford hope this makes things a little clearer

Each flat has an individual 22mm PVC about 1ft long from the floor to 15mm copper then stop cock then water meter then up into cavity into each of 3 flats

I believe the earth potential will be from the local PME supplying the flats, the pipe work will/should be bonded back to this inside the flats

The landlords cu, next to all the pipework in the cupboard outside is supplied via a PME supply from another block

so a potential difference should exist between the pipe work and the landlords supply and cu

I am considering binding the pipe work to the cu and back to the local PME but wanted other opinions first
 
Bond the exposed copper pipe to the landlords CU in each of the buildings. These copper pipes will probably be earthy from the buildings they are run in, especially if passing through, or run in floor slabs/columns etc...

When talking about concrete framed/constructed blocks of flat's, it doesn't matter if the incoming water supply is plastic, all flats metal water supply pipes should be bonded back to the flat's CU.
 

Reply to eicr flats bonding situation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
140
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock