Hi all, it's been a while but been busy in work and setting up my fledgling company I have a question, have a eicr tomorrow on a ground floor ex council flat. Had a look round earlier and can't find the main equipotential bond to the water but it is visible at the met in the db, if the bonding is under 0.05 ohm near the stop clock, with the gas bond disconnected can I class this as a c3? The supply is tt BTW not that it should matter, any advice greatly appreciated
 
You have no way of knowing the conductor at the MET is the water bond. Of course you can check it's continuity but this won't prove much except it has a connection to earth.
You don't own a rusty VW Golf by any chance.
 
Haha, I own a vw polo but far from rusty! I hope you are not implying I'm a cowboy I'm just asking a tricky question, OK so c2
No no it was from a previous thread I posted about seeing this rusty car in Port Talbot and I saw your location.
 
How you Code it is up to you and whether through tests you deem it requiring urgent attention.
 
No, I think you need to carry out some tests and you may find the conductor with a bit more investigation, all this before you decide on a Code.
 
Didn't spot the tt bit. There is every chance that tests would theoretically suggest it is a water bond by disconnecting and reconnecting it.
 
Agreed, just dont want to charge extra to install a bond from the db, although wouldn't be much cost - about 15m cable plus trunking, just been having a mare lately, 2 Rcd faults in a week or so, one a mem board with a functional earth causing probs, as I said a new business, just want to ensure everything is cosher, hanks for all replys
 

Reply to Eicr no visible main bond to water services in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi guys, sorry if this has been asked before. I’m currently in a flat where the tenant queried the water bonding. There’s a 6mm green and yellow...
Replies
4
Views
2K
I have a new combo meter box and 200A main shut off installed outside professionally. It has 4/0 service line coming into it and I have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock