Not sure what advice your asking for here, was there any particular parts of the EICR you were scratching your head about?.. luckily their is a nice concise section of the regs dedicated to such special locations so as long as your aware of the general requirements of the BS7671 and the special location requirements then you should be ok.
 
You need a detailed discussion with the swimming pool manager and maintenance manager to agree a schedule of circuit outages and power outages.
You also need to agree some limitations, such as lighting being off could be dangerous in such an area so live testing only or some such.
 
Cheers guys. My poor english Darkwood.... Arrived at the pool, 100mA main switch protecting everything. Do I not recall swimming pools should be TT?
 
Agi have certain restrictions of earthing systems.

There are no considerations for earthing restrictions for swimming pools. Just be aware of


  • Zones
  • Lot if use of SELV circuits
  • IP ratings for boxes, enclosures etc
  • BS for underwater lights
 
Start with a risk assessment. Rather assuming this is a public pool and not a private one, as it's in use all the time....just wondering as you've questioned the type of earthing in use. Getting at least the lighting tested out of hours would be the best option (first thing in the morning before the pool opens, or negotiate a late opening for the morning of testing)....having the lights go out when someone's going off the high board wouldn't be good.
 
Only the room containing ths swimming pool is covered under the special location the rest of the building is just a standurd installation open to the public just not sure about the changing room areas
 

Reply to EICR on local swimming pool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hey guys this is my first post on this site. Just got my design project It's a swimming pool hotel and cafe. I haven't got a clue where to begin...
Replies
10
Views
2K
Hi, I'm trying to understand legislation in the UK for using an air pump in conjunction with a swimming pool with regards creating and supplying...
Replies
2
Views
926
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
807
My customer wants to be able to switch his heat pump (3.5kW) for his swimming pool on and off remotely, he also wants to be able to set times for...
Replies
8
Views
623
Any ideas for an appropriate wall heater for school swimming pool changing rooms? (well detached from pool area but will still have wet bodies in...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock