Carried out an EICR today few things noted down to do,there is a 10mm equipotential bond on water and gas services. BUT the gas is bonded at the meter under the stairs and 2 inches down it enters the solid floor. also in the lounge there is a small gas pipe that comes out the wall to the fire and a pipe that comes out the wall in the kitchen to the cooker, my question is do i tell customer each point were it comes out in the rooms it needs a 10mm earth bond.
or would you guys ignore it cause its earthed at the gas meter.
i had an assessor raise the reg on corrosion to pipes on a new build but this time its not a newbuild and suppose this is relative to what he said.

kind comments only lol
 
I think your assessor is talking out of his ars*
It has to be bonded per regs , talk of corrosion is neither here nor there.
 
Carried out an EICR today few things noted down to do,there is a 10mm equipotential bond on water and gas services. BUT the gas is bonded at the meter under the stairs and 2 inches down it enters the solid floor. also in the lounge there is a small gas pipe that comes out the wall to the fire and a pipe that comes out the wall in the kitchen to the cooker, my question is do i tell customer each point were it comes out in the rooms it needs a 10mm earth bond.
or would you guys ignore it cause its earthed at the gas meter.
i had an assessor raise the reg on corrosion to pipes on a new build but this time its not a newbuild and suppose this is relative to what he said.

kind comments only lol

I suppose this assessor also requires that where any plastic water pipe is installed a bond is required if it changes to copper again!
 
There could be concerns if the pipe was entering the building at various points, rather than emerging from the structure at more than one place

Extraneous definition = existing on, or coming from the outside
 

Reply to Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Doing an EICR on a commercial install, there’s a copper pipe comes down a pipe chase with the stop cock fitted onto it, it’s then pvc pipes that...
Replies
2
Views
288
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
420

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock