Discuss Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

H

hsuelec77

Hi,

I carried out EICR on a rental property yesterdsy, i don't carry out many. i've only tested 25% and inspected 20% everything was ok, because theres no previous records should i carry ou 25% next
year or in 5 years time or change of tenant?

Thanks

Harry
 
No previous records, so it may never have been inspected, i would do a full test, change of tenant, can just be a visual and quick zs & rcd ze
 
I carried out EICR on a rental property yesterdsy, i don't carry out many. i've only tested 25% and inspected 20% everything was ok, because theres no previous records should i carry ou 25% next
year or in 5 years time or change of tenant?

Harry

As there are no previous records, i would carry out full I&T
 
No Previous records etc. = Always Full EICR for me.Even when minor work has been carried out, would you put your name on a certificate
stating that everything is OK? , without full tests.No, me neither!
 
I've done 2 EICR's recently where the previous records are available:

1. Last test was a "quick" test - the PIR listed all circuits but I doubt they actually tested all circuits in a "quick test" and in fact 1 socket circuit didn't have continuity on the neutral

2. Last test was a full test prior to purchase, organised by the seller. I doubt the tester was even taken out of the bag. For example the "end to end" readings for the sockets circuits were all "100", and yes thats for L, N and CPC and the IR tests were all 100+
 

Reply to Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
830
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock