Hi all need some advice when filling out test results on eicr's after carrying out live zs tests do you leave out R1 R2 column as in a lot of cases the measured reading is below ze value do you just make a note that it is a measurement and not a calculation?
any help appreciated
 
But how can you work out r1r2 from zs when it's not a true reading regarding service earths? If measured was below the ze what would you suggest? Thanx for response btw
 
Hey guys I hear what your saying but I know guys who carry out live zs tests and work out r1r2 from measured ze now I was always told zs - ze does not equate to r1r2
 
Well they're as deluded as the man at Megger that decided you can work it out as well and put this interesting feature on a meter (17 series, released fully tested)
 
The equation your looking for is Zs = Ze + (R1 + R2). You can not transpose this to work out (R1 + R2). i.e, you cant deduct the measured Ze from the measured Zs to get an (R1 + R2) measurement!!
 
well well well....
never ceases to amaze does it..
so some out there who are evidently teaching..in some form or another are putin it about that R1 R2 can be acheved by deducting a Ze from Zs....lol...
and i`v heard this before...
 
well well well....
never ceases to amaze does it..
so some out there who are evidently teaching..in some form or another are putin it about that R1 R2 can be acheved by deducting a Ze from Zs....lol...
and i`v heard this before...

I was taught to do this!! Except on TT!
Just to be clear I do not do this now!
 
whats the issue here...?
if you cant do cross connetions at the board (over congested)...then cross connect at a socket outlet....
or as has been said....limitation...

only need to do end to end for EICR dont need to do cross link connections as the installation has power and polarity can be checked when doing ZS.
 
And in fact, maybe even less than that; ultimately what is to be done is defined upfront, if it is just to do IR tests on one circuit and a Ze, then that is what will be done!! The rest isn't part of the agreement.
 
I was testing as a 2nd year apprentice, so it had barely been covered at college. My 'mentor' taught me to do it like that. But...what do u expect, company of at least 20 qualified electricians and maybe 2 had 2391, but hey as long as boss sat behind a desk co-signed it!!
Umm, it must have been college that taught me right, never would have passed exams otherwise. And since things have been in my own name I don't like to cut corners.
 

Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
971
OLDBOY
O
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
785
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock