Davem
Right guys first EICR found some C1&C2 codes obviously once thee have been rectified what certification do you give the client once a satisfactory ??
Discuss Eicr in the Electrical Forum area at ElectriciansForums.net
An installation cert/minor works referenced to the EICR
Thanks Trev with regards t that, I have a hob plug in a socket, shower on a to small of a breaker, no blanks in consumer unit etc. how would I go about filling the minor works cert in. I ask because I'm not really changing the wiring I'm just rectifying the problems, would there be a need a test again if I'm simply changing a breaker ?? Thanks again Trev
I don't like the sound of the junction box, should be on an outlet. Assuming the wattage is ok for a 32 amp supply then there's nothing wrong there and if the oven is less than 2KW then the recommendation for a dedicated supply doesn't apply.Shower is 10.5kw fitted with 10mm cable on 40amp mcb, for the hob it's supplied from a 32amp breaker in 6mm junction box to a double socket hob and oven plug in.
so..Thanks Trev with regards t that, I have a hob plug in a socket, shower on a to small of a breaker, no blanks in consumer unit etc. how would I go about filling the minor works cert in. I ask because I'm not really changing the wiring I'm just rectifying the problems, would there be a need a test again if I'm simply changing a breaker ?? Thanks again Trev
so...Shower is 10.5kw fitted with 10mm cable on 40amp mcb, for the hob it's supplied from a 32amp breaker in 6mm junction box to a double socket hob and oven plug in.
so...
you know that MCB will hold for upto 1.45 X its I N for upto an hour before it lets go dont you...
whats the installation method of the shower cable?