Stephen Waterworth

Good evening,
Some advice please. The heating we had in our bathroom is no longer working and the option open to me is installing an electric radiator in there. The location best suited to this is going to be close to a free standing bath. I have enclosed a photograph of the proposed location.

I know that there are lots of conditions when installing anything electrical in the bathroom (although, as a non electrician) I am not sure exactly what they are. Would you be able to advise on what I would need to consider.

The radiator I am looking to install is a closed mild steel 1000mm width electric radiator from VogueUk, image attached also

Your advice would be greatly appreciated

Regards

Steve
London

Electric radiator in bathroom question B6D7F0B1-B89F-4A43-8C5E-D5E2025A6025 - EletriciansForums.net


Electric radiator in bathroom question 81A4558A-3B0E-4DEC-B750-2EA183249706 - EletriciansForums.net


Electric radiator in bathroom question 78596825-38B6-408F-9BD0-9A6A44D89C2F - EletriciansForums.net


Electric radiator in bathroom question 8BBF2AF1-5149-4C82-ABF1-929A2A04BECF - EletriciansForums.net
 
if that blank plate covers what may have been a socket, if it'd 600 mm from bath, you could fit a FCU.
 
Hi Telectrix thanks for the response. Yes that plate is a socket, having just measured it from the rim of the bathroom to the plate, it is 630mm. I will get an electrician in to do this but just wanted to know some details about whether its feasible first of all. Dumb question, is fitting an FCU straight forward.
Thanks
Steve

Electric radiator in bathroom question IMG_5499 - EletriciansForums.net
 
What is the measurement of A (green line)?

Electric radiator in bathroom question IMG_5499 - EletriciansForums.net


Also make sure the controller is furthest away from the bath. May seem obvious but people have made that mistake in the past.
 
There other consideration is an RCD protected circuit. Otherwise it’ll work a treat.
 
As it is in zone 2 it must be suitable for use, check with the manufacturer.

Circuit must have 30mA RCD protection and accessories must be IPX4.
 
Great thanks Strima, Rpa7, Buzz and Telectrix. That all sounds positive. I will check with the manufacturer in relation to Zone 2. There is an RCD on the main board downstairs(I know there is a tech name for the board)
Thanks again
Steve
 

Reply to Electric radiator in bathroom question in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock