Search the forum,

Discuss ELECTRICAL INSTALLATION CERTIFICATES in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 138473

Hi

When filling out EIC forms under a few sections (design, construction) it asks to fill in the empty line with dates for an amendment of BS7671:2018.

Will this date be 2020 now as the first amendment has been released.

I was told to N/A this part by a tutor.

Thanks.
 
A question on disconnection times for new distribution circuits.

I have been pulled up by the NIC for not proving to meeting disconnection times on two different certificates, highlighted below.

The single phase circuit is from a TN system and supplies a converted bus using a TT system. The cable has had the SWA and CPC isolated in an insulated box, using only the local earth stakes and bonding.

The 3 phase circuit is from a TN DB to a new DB in the same building.

From the NIC - "provide evidence showing that the two Sub mains circuits installed at the two sites attended meet disconnection time stated in regulation 411.3.2.3 and 411.3.2.4"

The below apparently does not satisfy the requirement, and I'm just not seeing the issue.

Any help greatly appreciated.

Mick

1628504517263.png


1628504606218.png
 
Perhaps they want to see your design calcs although if the figures used are from the BBB or OSG no lengthy design calcs should be necessary!
May have to ask your inspector to be more specific!
 
Were they expecting to see the 80% figure of 0.69 ohms in the max permitted box?
The 2nd one is a tad close but within it.
Looking at the 2nd certificate, the other thing that might be viewed as suspicious is that by deduction the first two circuits suggest a Ze of 0.21 ish ohms and the 3 phase circuit suggests a Ze of 0.52 ohms. Something doesn't quite add up?
 

Reply to ELECTRICAL INSTALLATION CERTIFICATES in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock