Discuss Electrical installation design guide in the The Welcome Forum area at ElectriciansForums.net

Reaction score
101
Have been sizeing up the size of armour on diffent SWA cables to make sure they are suitable to be protective conductors. Come across table 8.8 page 100 .on this table it says maximum bs88 fuse size (for example) 120mm 4core is 500a, when it also says current carrying capacity is 335 method c and 353 method e.
Is this just one of the many mistakes in these books or I missing something
 
Have been sizeing up the size of armour on diffent SWA cables to make sure they are suitable to be protective conductors. Come across table 8.8 page 100 .on this table it says maximum bs88 fuse size (for example) 120mm 4core is 500a, when it also says current carrying capacity is 335 method c and 353 method e.
Is this just one of the many mistakes in these books or I missing something
Because motors start with a spike in current, you want slow blow fuses much larger than the FLA of the motor or the conductor. American code allows you to size the fuse or circuit breaker at 2 or 3 times the size you would use based on the FLA of the motor.
As for using the armour of SWA as a CPC, this is allowed for all 3 phase circuits.
 
I get that motors pull much more at startup (a few seconds at most ) but this table suggests that a 500amp fuses can protect a cable rated at 335 amps. As for armour being able to be a protective conductor on all size cables this is not true .
 
Any motor circuit over 0.37kW must include thermal protection against overload. So where as the fuse is say 500A the thermal protection will protect the cable and the motor from currents higher than they are rated.
 
So in a factory an main cable feeding a bussbar system feeding lots of isolators feeding lots of different loads and motors will not have thermal protection ,so sticking a oversized fuse in the main isolator may not be a good idea
 
I don't have it on me , but am sure in the iet earthing book it list diffent size SWA and some of them don't have the correct CSA to be used as a protective conductor .
 
I don't have it on me , but am sure in the iet earthing book it list diffent size SWA and some of them don't have the correct CSA to be used as a protective conductor .
I don't have it on me , but am sure in the iet earthing book it list diffent size SWA and some of them don't have the correct CSA to be used as a protective conductor .

Did you get the downloads?
 
Can't open it pete . what it say am guessing am wrong
Sorry I did it 3 times wasn't sure I had got it, it is a pdf of SWA cable szes in conjunction with the size of the armoring and it's suitability size wise to be able to be used as a cpc, I 'll have another look. PM me your email and I'll try and send it that way
 
Any motor circuit over 0.37kW must include thermal protection against overload. So where as the fuse is say 500A the thermal protection will protect the cable and the motor from currents higher than they are rated.
Rob, when we continuing reading Article 552.1.2 it says "this requirement does not apply to a motor incorporated in an item of current using equipment complying as a hole with an appropriate BS." which means if you have a motor which is part of a bandsaw or other machine 552.1.2 does not apply. right?
 

Reply to Electrical installation design guide in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi, I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working...
Replies
6
Views
1K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
538
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock