Discuss Electromagnetic effects , star / delta motor wiring ? in the UK Electrical Forum area at ElectriciansForums.net

JD6400

-
Mentor
Arms
Reaction score
742
I occasionally come across reasonably sized ( not for some of you , I know ! ) star delta motors that have been run in 2 x 3core swa .
Now after looking in to this in the past , it has been suggested that as they tend to be only on motors up to 30kw or so , and as the loading per phase will be near on equal the effects are not worth even considering !?

That said , it is just wrong to do this , is it not ?

What do others think .
 
Not really, think about 2 x 3P 3 core SWAs leaving a ferrous DB. The phases are perfectly balanced so no room for eddy currents to appear. Same for YD starting IMHO. The only thing I would say is that I'd like to see them run together.

Someone is bound to find a reg that proves me wrong though :D
 
I sort of see what you mean , but this is u1,v1,w1 on one leg with u2,v2,w2 on the other , out of the starter .
And although it is not a lot , I normally see the windings differ by an amp or so .
I have been far from top form of late , and just can not seem to get my head around it at the moment .
 
I sort of see what you mean , but this is u1,v1,w1 on one leg with u2,v2,w2 on the other .
And although it is not a lot , I normally see the windings differ by an amp or so .
I have been far from top form of late , and just can not seem to get my head around it at the moment .

I guessed that mate, my point was that if you can run two 3P motors out of one DB with ferrous material inbetween then the same would apply to running the same 3P motor out of one enclosure provided the phases are equally balanced in each cable ie. you wouldn't want u1, u2 and v1 in one cable and v2, w1 and w2 in the other.

I can't honestly see any problem at all with this set up :)
 
Well, I don't quite see how the supply to an assembled machine can have cables that are feeding a star delta fed motor.

I'm just trying to make the point that the whole electrical world does not revolve around BS7671.
In fact, it is one of the standards most weakly backed up by statute law.

In fact, really as has been said, there is little issue, from an eddy current standpoint.
Personally I would use a 7 core cable, and never SWA, as it is not suitable for connection to vibrating equipment.
I would be more concerned about the earthing integrity if it was SWA connected to a vibrating machine.
 
I guessed that mate, my point was that if you can run two 3P motors out of one DB with ferrous material inbetween then the same would apply to running the same 3P motor out of one enclosure provided the phases are equally balanced in each cable ie. you wouldn't want u1, u2 and v1 in one cable and v2, w1 and w2 in the other.

I can't honestly see any problem at all with this set up :)


I do understand what you are saying , but I don't know why I just can not except it !?
It just feels wrong !
And of course I know that has no standing when it comes down to the crunch , but surely I am not the only one that sometimes thinks the same about some scenarios ?
 
Well, I don't quite see how the supply to an assembled machine can have cables that are feeding a star delta fed motor.

Define 'machine' lol.

I'm just trying to make the point that the whole electrical world does not revolve around BS7671.
In fact, it is one of the standards most weakly backed up by statute law.

You are quite right, you make a very good point.

In fact, really as has been said, there is little issue, from an eddy current standpoint.
Personally I would use a 7 core cable, and never SWA, as it is not suitable for connection to vibrating equipment.

I have always favoured flexible conduit for final connection, but I guess it always depends on the application of the motor and any requirements the customer may have. I personally can't see the vibration of any decent motor being bad enough to work loose a decently glanded connection, if the vibration is that bad I would say there is a mechanical issue that needs addressing!

- - - Updated - - -

I do understand what you are saying , but I don't know why I just can not except it !?
It just feels wrong !
And of course I know that has no standing when it comes down to the crunch , but surely I am not the only one that sometimes thinks the same about some scenarios ?

It feels wrong because you would always install using a 7 core cable! lol
 
Define 'machine' lol.

I have always favoured flexible conduit for final connection, but I guess it always depends on the application of the motor and any requirements the customer may have. I personally can't see the vibration of any decent motor being bad enough to work loose a decently glanded connection, if the vibration is that bad I would say there is a mechanical issue that needs addressing!

It feels wrong because you would always install using a 7 core cable! lol

Ok, the definition of "machinery" electrical equipment is easy, covered by BS EN 60204-1, and not BS7671.

If it is an assembly of linked components and is not part of the fixed electrical installation then it's machinery.

I do sometimes use flexible conduit.
However, what do, you, put "inside" the flexible conduit?
6491 type wire?
If so, again not suitable for connection to vibrating equipment.

Any rotating device vibrates.

Oh & I think it was me who said 7 core not the OP.
 
More to the point , why do it this way in the first place ?
I mean it is twice the work over just one 7 core !?

This is the obvious issue that you can't get your head around. I'd like to think that any decent spark would use one cable or one method of containment over two cables, still, I can't see an issue regs wise or principle wise with the latter of those two options.
 
Ok, the definition of "machinery" electrical equipment is easy, covered by BS EN 60204-1, and not BS7671.

If it is an assembly of linked components and is not part of the fixed electrical installation then it's machinery.

I do sometimes use flexible conduit.
However, what do, you, put "inside" the flexible conduit?
6491 type wire?
If so, again not suitable for connection to vibrating equipment.

Any rotating device vibrates.

Oh & I think it was me who said 7 core not the OP.

Our standard set up on a dryer would be to come from the control panel in 7c swa (with a 2c controls swa for the isolator indicator switch if applicable with the control panel spec) on tray up to a 6 pole isolator then out in to the dryer in armoured flexible conduit on swivel top hats with what I call controls cable ( fine AWG ) in that with all terminations crimped with which ever one is appropriate for the motor .
 

Reply to Electromagnetic effects , star / delta motor wiring ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi and thanks for any replies. I am predominantly an install electrician and don't have a lot of experience dealing with motors so any help would...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock